Just a quick note mate, if you carry out an IR test on the whole circuit, or indeed the whole installation, you shouldnt need to test every cable individually (presuming that the 'whole circuit reading' was clear of course).
A 'figure of 8' test is very important as well, especially on the neutrals, to make sure that you have the correct neutrals connected to the correct RCD. Personnaly, I would connect the live and neutral, and then check all sockets on that circuit. I would also test all sockets on the OTHER circuit as well, to try to eliminate shared neutrals. An IR/continuity test between the different neutrals at the board, and in the field may be usefull as well.
If your unsure, its always best to carry a martindale, or volt stick (ducks for cover) when you are sticking your IR tester on something which 'could' be live.
Not sure what the first line of your post means.
Are you refering to the original post or the one tonight,basically I had a rcd that covered the downstairs ring tripping all the time ,I did some quick tests and found some errors which I need to correct .I am hoping something will become very apparent and soon.I spoke to a sparky friend tonight and he has suggested that every socket be removed and I check as above.He is a senior lecturer and guess he know whats what.Very handy to bounce ideas off him with technical issues every now and then.The shared neutrals seems to be a common mistake so I will check for that first,thank you.For info he immediately suggested crossed rings.Just had a text come in and the client now wants all new switches and sockets throughout the whole house,now to figure out a price incorporating a day testing as well.
Regards,
) when you are sticking your IR tester on something which 'could' be live.