Hi guys, as the title suggest how do u test the R1 R2 value or R2 continuity if the sockets are earthed via the metal conduit?

Thanks guys
 
nicsin, I take it you haven't got a problem with R1 & R2 on a circuit wired in T&E.
Conduit (or Trunking) is just a conductor like the bare core in T&E, nothing magical or mysterious about it!
Remember, you'll invariably get much lower R2 readings than T&E.
 
nicsin, I take it you haven't got a problem with R1 & R2 on a circuit wired in T&E.
Conduit (or Trunking) is just a conductor like the bare core in T&E, nothing magical or mysterious about it!
Remember, you'll invariably get much lower R2 readings than T&E.

Much, much lower!! lol!!
 
I know I'm cracking on a bit and do tend to have senior moments but I'm sorry to say I can't see what the problem is.
 
Yeah but normally you would separate the c.p.c with twin and earth and measure between??

If your only cpc is the Conduit then you cant do a R1 + R2 due to parallel paths. Take your R1 inspect teh the conduit throughout and prove conitnuity.

If you have a seperate cpc within and you can isolate the cpc throughout from the Conduit then yes you can record a R1 + R2.

Take a Zs reading at the socket and thats about it.
 
I know I'm cracking on a bit and do tend to have senior moments but I'm sorry to say I can't see what the problem is.

Total lack of experience is the culprit here!! These day's if it isn't T&E or SWA installs, the head scratching starts!! lol!!
 
If your only cpc is the Conduit then you cant do a R1 + R2 due to parallel paths. Take your R1 inspect teh the conduit throughout and prove conitnuity.

If you have a seperate cpc within and you can isolate the cpc throughout from the Conduit then yes you can record a R1 + R2.

Take a Zs reading at the socket and thats about it.

At last!! lol!!

I was wondering when or even if someone was going to come up with the correct overview of testing a conduit installation. Though why anyone would install a separate CPC in a conduit installation still eludes me!! lol!!


Or you could hire a Ductor that delivers 25amp to test the conduit
smile.png



I wonder how many of the younger members here even know what your talking about, let alone ever seen or used one?? ...lol!!​



 
Was it also known as a "Clare" tester, have distant memories of sparking conduit joints in our apprentice training centre

Yes!!

Normally came in a wooden case, but have seen metal cased units too!! Last time i've seen one being used in the UK was 20 years ago, when i was witnessing the testing and commissioning of a large shopping centre. Pretty pointless testing continuity on this installation, as the whole building was metal framed throughout and all the landlords (for want of a better term) electrical installations, metal containment, etc was solidly fixed to this frame work. Not a single failure, or even remotely close to a failure was seen throughout the whole building!! lol!!
 
I use a Clare tester in the workshop for proving bonding on the cabinets that we manufacture; that gives a wee spark if the contact isn't good enough!
 
I use a Clare tester in the workshop for proving bonding on the cabinets that we manufacture; that gives a wee spark if the contact isn't good enough!

They can give you more than a Wee Spark just by making a slowish contact to a solidly earthed/bonded testing point!! lol!!

I've engraved my name on the inside of 20 X 20cm galvanised pull boxes with these testers in my youth!! lol!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
r1 r2 through conduit
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
nicsin02,
Last reply from
Engineer54,
Replies
19
Views
4,629

Advert

Back
Top