overjoyed at the idea of stepping in and out of a metal box with 100mA
True but as long as you trust the earthing (and any supplementary bonding if you like) you should be disconnected within a few seconds if there's a fault, and the touchouch voltage shouldn't be too high.
I'd be more worried about all that 17kw of uv coming from the tubes tbh, it'd be factor 50 for me!
 
  • Like
  • Agree
Reactions: DPG and Wilko
See #13 - The OP says each bed is connected to its supply by a 5 pin interlocked plug and socket. Is this acceptable if a 100mA RCD is used? I don't know if it is and whether instead each bed must be 'hard-wired' in.
 
As above, power circuits with sockets of 16A and below require a 30mA RCD.

Presumably if he has 32A MCB’s then he is using 32A sockets.
 
  • Informative
Reactions: marconi