I have just noticed the insulation surrounding the earth going to 2 machines at work has melted close to the connection points of the machine. I don't know why this has happened but I do know there is alot of static built up on the machines due to the materials used in the conveyors. Would this static have caused the insulation to melt? How do you discharge the static from these machines if the earth is not doing this? :confused:
 
stupid i know , but its not heat from the machine as you say its at the conection point. Not trying to be funny just a thought.
 
No, it's connected in the control panel and it's nowhere near hot enough to melt it. It melted to about 5" from the connection point.
I'm going with the static theory until i'm proven otherwise!
 
No, it's connected in the control panel and it's nowhere near hot enough to melt it. It melted to about 5" from the&nbsp;connection&nbsp;point.<br>I'm going with the static theory until i'm proven otherwise!
 
Do you have access to a DC clamp meter? It may give you some clue if it’s static. To be honest continuous static build up doesn’t normally give that high a current to do any damage. Multiple bonding points spring to mind if static I that bad a problem, it has to be done on coal and gas handling plants.

Another thought, as it’s burnt in one specific area has something hot been spilt on it?
 
Last edited by a moderator:
Do you have access to a DC clamp meter? It may give you some clue if it’s static. To be honest continuous static build up doesn’t normally give that high a current to do any damage. Multiple bonding points spring to mind if static I that bad a problem, it has to be done on coal and gas handling plants.

I have a DC clamp meter - but what do I do with it?! When you say multiple bonding points, do you just mean I should earth a few more points of the machine?
 
Although I don't believe it this to be the problem, I worked on a paper laminating machine, in a previous role, in which hydraulics were used to move the printing/gluing decks. A fault developed on a 110vac valve coil for one of the decks. The 110vac supply was 55-0-55v. The coil fault appeared on the -55 side of the coil supply which was via a 'neutral link' as opposed to a fuse terminal. The earth wire insulation melted all the way back to the Tx. Wow.

Any electric welding been done on these machines lately?

Is the connection soldered?

Is the connection tight?

Is the connection to 'bared' metal?

.
 
Last edited by a moderator:
All connections are tight and are not soldered. There was some welding done, but not near the machine in question and not on the same circuit. Do you think welding carried out close to the machine would cause this? I am going to increase the size of the supply cable and therefore the earth connection. Any thoughts?!
 
Nice one Silva. Stray earth welding currents, should have remembered that one. I’ve had umpteen SWA’s and earths toasted by Muppet welders not earthing properly.
 
Thanks guys - so ye reckon it's stray welding currents? Sounds like a logic explanation. I will replace the damaged cable and see how it goes. If I have welding going on I will monitor it and see if it has any effect. I'm going to put that in the problem solved folder, for now.
 
You will find a welder will just plonk his earth return any where near the machine, not necessarily on it.

One company I worked for came up with a brilliant idea. All fixed welding sets had to have an earth wired from the welding return terminal. The welders thought this was great, they didn’t have to drag an earth return out because it was connected at the welding set and the via the plant cabling CPC’s. The idea lasted about a fortnight before I went around the plant welding sets cutting the permanent return earths off.

You think plumbers are morons? Welders are in a class of their own!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Static and a melted CPC!
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
gerard,
Last reply from
gerard,
Replies
11
Views
1,954

Advert

Back
Top