we use them all the time for smaller wireWe don't use Fire nu... sorry, I mean Wire nuts over here for starters.
what would a service look like on a single family dwellingDo y’all run conduit or approved cables
Very good information and I’ve wired quite a few European equipment and yes all the wire was in millimeters with European drawings which uses different symbols. I was wiring a machine for a man from Finland and he couldn’t understand that if we could we had to run it in pipe. He was a cool guy just trouble with communicationWhy not grab yourself an old copy of our equivalent of the NEC (BS7671, aka the 'wiring regs'.) It would take a long time to run through each difference but you could get most of the story even though the book isn't fully up to date.
One of the main differences is that BS7671 is less prescriptive than the NEC. There's less talk of how many wires you may join in a particular size of box, and more emphasis on calculating and evaluating the characteristics of each cable and material and assessing the suitability for yourself. We're also much more into testing. Not only volt drop and ampacity but earth fault and short-circuit loop impedances and their corresponding fault currents are all assessed for every circuit before installation, and then tested afterwards and compared to the curves of the breakers to ensure they will operate correctly, before a circuit is considered ready for use.
Some important supply differences:
Our supplies are 50 Hz (=cycles), so induction motors run at approximately 1000, 1500, 3000 rpm instead of 1200, 1800, 3600.
Domestic services are 230V single phase, typically 100A. Line (=hot) and neutral are provided by the network, sometimes earth too, otherwise a rod is used. Only the network operator is allowed to combine (=bond) neutral and earth, they may not be linked in the distribution board (=panel). Split phase (as in typical US services with two lines each 120V to neutral and 240V between them) is never used, although a very few old rural installations where the high voltage supply is only single-phase have 240-0-240 with 480V between lines.
Industrial and commercial services are normally 3-phase 4-wire star (=wye) 400V line-line, 230V line-neutral, from the same distribution cables as the domestic single-phase but with all three phases present instead of just one. There are no open delta, edge grounded or high-leg asymmetrical configurations. An increasing number of larger industrial loads are 690/400V.
More later on materials and circuits...
Do y’all have to draw permits and when you are finished get it inspectedVery good information and I’ve wired quite a few European equipment and yes all the wire was in millimeters with European drawings which uses different symbols. I was wiring a machine for a man from Finland and he couldn’t understand that if we could we had to run it in pipe. He was a cool guy just trouble with communication
The manufacturing plants are mostly 480 vac delta ungrounded systems. That makes you have to lnstall a lot of transformers to get you 208/120 on the secondary side of the transformers. We do have plants that have 480 vac 3 phase star connections alsoOn single family dwellings it’s 240vac single phases with 2 hots and a grounded conductor-and we, not the power company drive 2 rods at the service 6 feet apart and bond the neutral bar in the main panel and bond the water lines if there is galvanized piping When you have to bury wire it has to be 24 inches to the top of the pipe
What do spured fuses meanPut up a list of your terminology and members will see if they can give interpretations.
The correct terminology is fuse connection unit which are often called spurs as they are often used for spurring from a ring final circuit. It is essentially a double-pole switch which incorporates a fuse, up to 13A to protect the load side circuit.What do spured fuses mean
This question probably hasn’t been answered yet as it’s a contentious and complicated subject. In short experienced and competent sparks are expected to test and certify their own installations. Certain domestic work has to be notified to to the local authority.Do y’all have to draw permits and when you are finished get it inspected
Depending on what you are getting a permit for it cost around $100.00. I worked out of town in another state and they charged by the amp which at that time we was working on a 4000 amp switch gear which I had to pay and it’s was around $ 650.00 US dollars and they would not take nothing but cash. Every state . County, and inspectors are different and have their rulesThis question probably hasn’t been answered yet as it’s a contentious and complicated subject. In short experienced and competent sparks are expected to test and certify their own installations. Certain domestic work has to be notified to to the local authority.
How much do you have to pay to draw a permit? Presumably that covers the cost of a third party inspection?
Depending on what you are getting a permit for it cost around $100.00. I worked out of town in another state and they charged by the amp which at that time we was working on a 4000 amp switch gear which I had to pay and it’s was around $ 650.00 US dollars and they would not take nothing but cash. Every state . County, and inspectors are different and have their rules
I don’t even know half of what you was saying
That's a switched fused connection unit, used for connecting a spur to.This is a "switched fused spur":
Do y’all not have panels with all your overcurrent and short circuit and run your wires the the devicesThis is a "switched fused spur":
View attachment 51111
This is a "switched fused spur":
View attachment 51111
is that a fuse beside a switch. Remember I’m in the US and trying to learn y’alls way of doing thingsThis is a "switched fused spur":
View attachment 51111
Do y’all not have panels with all your overcurrent and short circuit and run your wires the the devices
we do. we call them Distribution Boards. domestics are commonly referred to as Consumer Units.Do y’all not have panels with all your overcurrent and short circuit and run your wires the the devices
Thanks for the knowledge and helpwe do. we call them Distribution Boards. domestics are commonly referred to as Consumer Units.
We use breakers as our overcurrent protection not fuses
That's a switched fused connection unit, used for connecting a spur to.
Capital letter at the start, full stop at the end. Anything more complex than that and you're talking to the wrong guy.Now, now Andy78, that's a tad pedantic of you! LOL!
Plus, you ended your sentence with an unnecessary preposition. If we are trying to assist our American friend with the correct terminology for our superior electrical items, we should be careful not to let him think our grammar is inferior...
one phase is a much higher voltage to earth and called the hot wire, never seen that in UK.
Lucien I personally don’t use Delta 3 phase transformers. And you are right it’s useless to the work I do, the only use for it in my opinion is just 3 phase loads onlyI don't think we've ever used edge-grounded delta at all. It's a cheap way to rig up 3-phase on systems where the normal service is split-phase with both lines present in most installations. Because we only ever use split-phase in the absence of 3-phase (as our single-phase is 230V not 120V) we wouldn't have anything to gain from high-leg delta. And I think it is technically 'high leg' or 'wild leg' rather than 'hot', because hot just means line.
The T in TN is Terre, it's French.
Hot wire = live UK. Active Aus
No Split or Polyphase in UK generally used
I like the terminology and the way electrical is different in other countriesNo Hotleg Delta Transformer set ups in UK.
GFCI = RCD
Hot wire = live UK. Active Aus
Travellers = Strappers UK
Romex or NM = T & E UK, TPS Aus
No Split or Polyphase in UK generally used
Red, Black and Blue phase colours are Brown, Black, Grey UK or Red White and Blue in Aus
Receptical = Double or Single socket UK, GPO Aus
EMT - Conduit
No AWG cable sizing in the UK
Midget - Outlet of shallow depth
60hz - 50Hz UK and Aus