Hi all,
I am a BIG fan of the Wago connectors, but am I required to enclose them in a box? They seem to me, to be very well insulated in themselves....

????
 
OK. If I understand you correctly, It is a requirement to make sure the coloured insulation is enclosed in the box?
 
Are you telling me that the sheath of a 2.5mm T&E cable provides mechanical protection? Surely not..
 
In the regs it states that single insulated cables need mechanical protection. Enough said.

All views are my own, remember I'm just the apprentice
 
BS 7671:2008 Ammended to 2011 Reg:521.10.1 States Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking. This requirement does not apply to a protective conductor complying with Section 543.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X.

Seems very clear now, thanks micky86.

I can only conclude that the outer sheath of a 2.5mm csa T&E is considered to be a "Cable Trunking System" providing at least IPXXD or IP4X.
 
wx2 steel trunking buried in mrs jones's stting room walls, can you?ell, you can't have 2
 
BS 7671:2008 Ammended to 2011 Reg:521.10.1 States Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking. This requirement does not apply to a protective conductor complying with Section 543.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X.

Seems very clear now, thanks micky86.

I can only conclude that the outer sheath of a 2.5mm csa T&E is considered to be a "Cable Trunking System" providing at least IPXXD or IP4X.

No problem.... Now if only there was a thanks button..... Haha
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
The need to enclose wago connectors in a box
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
ARCElectrical,
Last reply from
Rockingit,
Replies
29
Views
34,370

Advert

Back
Top