Discuss The need to enclose wago connectors in a box in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

ARCElectrical

Hi all,
I am a BIG fan of the Wago connectors, but am I required to enclose them in a box? They seem to me, to be very well insulated in themselves....

????
 
BS 7671:2008 Ammended to 2011 Reg:521.10.1 States Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking. This requirement does not apply to a protective conductor complying with Section 543.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X.

Seems very clear now, thanks micky86.

I can only conclude that the outer sheath of a 2.5mm csa T&E is considered to be a "Cable Trunking System" providing at least IPXXD or IP4X.
 
wx2 steel trunking buried in mrs jones's stting room walls, can you?ell, you can't have 2
 
BS 7671:2008 Ammended to 2011 Reg:521.10.1 States Non-sheathed cables for fixed wiring shall be enclosed in conduit, ducting or trunking. This requirement does not apply to a protective conductor complying with Section 543.
Non-sheathed cables are permitted if the cable trunking system provides at least the degree of protection IPXXD or IP4X.

Seems very clear now, thanks micky86.

I can only conclude that the outer sheath of a 2.5mm csa T&E is considered to be a "Cable Trunking System" providing at least IPXXD or IP4X.

No problem.... Now if only there was a thanks button..... Haha
 
I can only conclude that the outer sheath of a 2.5mm csa T&E is considered to be a "Cable Trunking System" providing at least IPXXD or IP4X.

No, it is a sheath, hence why the Regulations refer to "non-sheathed cables". Therefore that does not apply to sheathed cables, such as twin and skin.
 
So . . . . .

Asking this another way, is it ok to fit a jb with the insulation showing on the outside or with the guards in the wrong place? Course not so what's the difference?
 

Reply to The need to enclose wago connectors in a box in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, As a householder I'm keen to add a double socket further along a wall to extend access in a different corner of the room. I'm connecting...
Replies
4
Views
457
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
689
Hi all, I am about to fit a light fitting and wanted some advice whether I should just connect the light cables into the correct terminal blocks...
Replies
2
Views
622
Hi All. Anyone got experience/usage of using the Quickfix Junction Box, with the Wago 221 Connectors ? https://www.quickfixjb.co.uk/...
Replies
8
Views
724
Hi all, I’m after some advice regarding use of Wago boxes for adding a spur off a ring final. Is it okay to use a MF Wagobox with 221 Wago...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock