I think you need to upgrade the whole CU area.. its time for whoever owns the mess to pay up..Should I upgrade 6mm E.
Thanks for your replies.
Once I found the problem I fitted 63a RCD as isolator in main DB with Henley Block.
Problem now is that 6mm E.
Thanks for all the replies.
I let a Sparky with some forty years experience connect Sub Main Cable at the origin of the circuit ( although he did send someone else to do it ).
My experience may be low but I'm learning at a great rate of Knots.
On Friday I isolated Sub Main at origin with 63a Rcd. The RCBO in extension DB has 100a Isolator.
The Line Conductor cable has a CSA of 6mm so that's 12mmsq.
The time/current graphs in Regs say 100a RCBO = 500amps.
500x5/115 = 9.72.
Going to run 10mmsq from extension DB to MET at origin of the circuit.
I never gave a thought to the work done at origin, why would I - it's been done by a qualified Spark!