A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?
 
what is the answer to this question please?

A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?

no calculations needed , just look up the value in max Ze tables in bs7671 for 16a type C
the value is the same for single & 3 phase.
 
Am i missing something! IE, OSG page 119 Type c 60898 16a max zs = 1.16 ohms, BS7671 page 56 Type c 16a 60898 max zs = 1.44 ohms.

The value in the onsite guide is 80% of the value given in BS7671, as it allows for changes in Ze etc. This is the value you should not exceed when designing and installing a circuit, hence why it is in the onsite guide!
The 100% value (1.44) is the absolute maximum value which would allow enough current to flow to trip the MCB/fuse etc. in the required timescale. i.e 0.4s
 

Reply to type C Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock