what is the answer to this question please?

A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?
 
what is the answer to this question please?

A 16amp Type C CB used to protect a three phase reduced low voltage circuit is subject to a maximum Zs value of?

How do I work this out?

no calculations needed , just look up the value in max Ze tables in bs7671 for 16a type C
the value is the same for single & 3 phase.
 
Am i missing something! IE, OSG page 119 Type c 60898 16a max zs = 1.16 ohms, BS7671 page 56 Type c 16a 60898 max zs = 1.44 ohms.

The value in the onsite guide is 80% of the value given in BS7671, as it allows for changes in Ze etc. This is the value you should not exceed when designing and installing a circuit, hence why it is in the onsite guide!
The 100% value (1.44) is the absolute maximum value which would allow enough current to flow to trip the MCB/fuse etc. in the required timescale. i.e 0.4s
 
Mike the mx allowed is 80% of the tabulated value though. Not nitpicking, discussing :)
Out of interest trev we allow 85% on EICR's, sometimes upto 90% if previous results are taken into account and show stable readings. The 100% value is the max allowable I believe. But you would always use 80% for design and installation.
 
The answer is 1.44 IMO, I don't write 80% values down on sheets myself, it asks for maximum values does it not?

100% agree! If the question is asking for the MAXIMUM allowable value then the answer should be the MAXIMUM allowable value, not the maximum allowable value minus 20%???
 
the 4 possible answers I have are as followers

A. 0.69
B. 0.2
C.1.15
D. 0.4
I think 0.4ohms. The question relates to reduced low voltage, which is a maximum of 63.5V line to earth. So, taking 1.44ohms for instantaneous operation at 230V line to earth, the value for 63.5V will be 1.44/230, x 63.5, =0.4ohms. Obviously, if the supply is lower than the maximum for reduced LV (not stated) then a lower Zs will be required. (Apologies for no line breaks.)
 
I think 0.4ohms. The question relates to reduced low voltage, which is a maximum of 63.5V line to earth. So, taking 1.44ohms for instantaneous operation at 230V line to earth, the value for 63.5V will be 1.44/230, x 63.5, =0.4ohms. Obviously, if the supply is lower than the maximum for reduced LV (not stated) then a lower Zs will be required. (Apologies for no line breaks.)

I think you're right. I'm gussing most of us (including myself) skipped the OP to chat about OSG Zs values vs BGB max Zs values.

A case of read the OP and definitely a case of RTFQ!
 

Reply to type C Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
862
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I live in Thailand and my home has 240v, 3 phase power supply. I want to add an electric car charger but first want to determine what the outlet...
Replies
0
Views
678
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
882
Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
Replies
2
Views
880

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top