Can someone let me know the wiring procedure when underflooring heating is being installed by flow and return piping,and seperate room stats are required for rooms.so six rooms and each room having its own stat which are wired and not wireless.
 
If it's a y-plan and there not piped individually with actuators for the stats to open them, the only way is all stats in parallel and if any one of them calls it will bring the whole heating side of system on, bit rubbish if this is the case.
 
You need to know what equipment he is installing in terms of manufacturer.

Underfloor heating for 6 zones will need a central controller that communicates with the room stats/controllers and controls the manifold valves. Depending on the manufacturer you could need:
simple T & E
4/5 core cable
or even ethernet type cable.
 
Depending on which type of Programmable stats your using, but for example if it was a heatmiser 12v system I would have a cat5 from each stat back to my wiring centre, then were ever your zone valves are, have at least 3 cores back to your wiring centre there. The wiring centre (UH1) would be near the manifold I hope, therefore your pump, pipe stat and zone actuators can all be surface...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Underfloor Heating
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
bluecallum,
Last reply from
MrTrance,
Replies
8
Views
1,366

Advert

Back
Top