colfair

Trying to fit a standard PIR using FSL conjnections method and cannot get the the resistance to change to 6K9 when PIR is activated! Can anyone help?
 
Check pir, some units dont actual have relay contacts. They used an old method of switch negitive on the nc wires.
To check this, out of circuit check NC tracks on back of pcb for a linked track between nc conections.
In circuit ie powered up, check nc connections for operation with meter.
 
Pyronix KX range are perfect as you can use them in all situations and both types of wiring and if you are using FSL then you can use jumpers to suit the resistance you require to each circuit
 
I'm not sure how, if it's as you say, a standard PIR, then it should be "compatible"....

For that panel, and FSL - you need a 4k7 resistor across your "alarm" terminals in the PIR (together with one of your FSL pair on one terminal only.... you then from the other alarm terminal wire a 2k2 resistor to the first tamper terminal, and then put the second FSL wire in the other tamper terminal. Provide power in the normal way. Close lid. Activate detector, voila.... 6k8 or 6k9 usually give or take 10%.

The 4k7 is a shunt resistor - when the device goes active, rather than simply going open circuit, it will increase resistance through the shunt. The 2k2 end of line is a monitor resistor - it sees the 2k2 value as a "closed" circuit - or one that is not active, not in trouble.

When the alarm circuit opens, 4k7 +2k2 = 6k9 (+-10%). When tamper is open, open circuit. When all clear 2k2. Simples.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
wiring PIR to scantronic 9651PD
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
colfair,
Last reply from
accordfire,
Replies
6
Views
6,988

Advert

Back
Top