Multiple consumer units

Discuss Multiple consumer units in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

E

ElectricEddie

Hi guys,

im currently in the middle of doing a rewire on a large domestic property which has a single phase supply, in total I will have 4 consumer units and a distribution board of some kind - also we do lighting control so all the light circuits are separated and going back to a Cbus lighting board which along with the cus will be in each divided zone.

I have run my feeds for my cus back to the distribution point in 16mm L/N and also run in a 16mm Earth to go back to the MET.

So my question is what sort of board is going to be best to have these 16mm feeds going to it im sure I'm right in thinking that they will have to be rcd protected as well as having the rcds in each consumer unit but correct me if I am wrong.

thanks

ed
 
This rewire should have had these decisions made at the planning stage. RCDs in series, or RCDs covering distribution circuits within the installation with the set up you describe is unbelievable to be honest.
 
There will be RCDs covering the distribution circuits that is the whole plan the only question I am asking is what type of board is going to be best to use
 
Could you advise what would be best to do please

Start again with the distribution circuits run so they don't require RCD protection to offer better division of circuits for the final circuit arrangements, and have a think about what sort of OCPD would provide the best discrimination for the distribution circuits bearing in mind the devices fitted to the final circuits in the sub boards.
 
The point been made here by Andy was its poor design to have submains RCD protected, you design to supply your submains in say a SWA which would negate the need for rcd protection then have a duel RCD split board or RCBO boards for the final circuits, your also in the middle of the rewire and your asking advice on design that should have been worked out long before you got to this stage..

Regardless how far on the job is we can try to help but first a few questions -
-When you say you have 16mm L/N + seperate earth ..what kind of cables and install method are the L and N.?
-You say the 16mm earth goes back to the MET - is this the earth for the submain in which case it would be better to put it in the earth terminal for that particular distribution way to limit confusion.
 
Last edited:
Ok that is very helpful thank you for your input, I will be able to calculate the sort of over current protective device easily enough via the Way I have arranged the circuits off of each sub board .it was only the distribution element that I was unsure of.

please know also that this job is still very much in the first fix stage so anything is changeable and no consumer units or DB's have yet been chosen.

in your opinion what would be the best way to run the distribution so that it needn't require RCD protection.

Thanks again
 
It's 16mm t/e with a separate 16mm2 Earth reference method 103 so through stud walls and joists etc my plan was to use the 16mm Earth in order to ensure my resistance was low enough to meet the ads times for each submain all submains having an Earth back to the main Earth at point of distribution
 
It's 16mm t/e with a separate 16mm2 Earth reference method 103 so through stud walls and joists etc my plan was to use the 16mm Earth in order to ensure my resistance was low enough to meet the ads times for each submain all submains having an Earth back to the main Earth at point of distribution

This method of choice would require rcd protection unless your somehow deeper than 50mm for the full run, like I mentioned before, if you can design your submain run or change the cable to be able to omit the rcd protection then its a better method.
 
This method of choice would require rcd protection unless your somehow deeper than 50mm for the full run, like I mentioned before, if you can design your submain run or change the cable to be able to omit the rcd protection then its a better method.


This is exactly what I thought. I have made sure that throughout the run I am more than 50mm deep due to the fact that all the walls have bee studded off so I have run behind all the stud work I'll measure out at all the shallowest points to double check tomorrow.

with this method of installation would I then just be able to run All the circuits from a single isolation point

either that or swap to swa

thanks very much for your help
 

Reply to Multiple consumer units in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock