Hi, I'm at a job where there is 4x16 amp sockets protected by 4x16 amp rcbos in a bollard, the customer now wants 6 amp rcbos cause he wants to limit what people are using can you do this? I suppose it will just trip if people use more than 6 amps
Yes.
You have answered your own question.
Do job, on certificate for circuit breaker change, note potential tripping caused by overload, submit with invoice ....
What a load of bollards
Yes you can do this and yes the circuit breaker will trip if overloaded. It will be a safe circuit within the design parameters of the wiring regulations.
Is this a practical approach, no, because it is effectively designing the circuit to fail and causing a circuit breaker to trip regularly is not ideal as they will have a much shorter lifetime and so need replacement.
Informative signage would help but it is still not ideal from a practical perspective.
Murdoch has the better, shorter answer, cover yourself.
These are the bollards, and thanks guys much appreciated
Okay, stupid question time.
Is this installation designed to supply something like a market stall? The reason I ask is because I see C type RCBOs have been fitted.
Yeah ok :) I should have said what types and sizes of appliances ...
You'd think after all my time on here and years of wading through City and Guild's ambiguous syntax, I would have learned to construct a concise and specifically worded sentence wouldn't you ?
More the opposite .... its wading through the antiquities of BS 7671 that I hate