PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house

Discuss PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

the University has several ... substations ... so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
I'm guessing DNO can supply an earth to a quality level they feel is ok, but within the installation Table 54.8 would say it needs 50mm copper, which is about 400mm steel. And 4 core 300 is about 320mm steel, so it wouldn't pass muster. Unless I'm talking rubbish o_O
 
Well I suggest you get a pet rat and train it to run through drain pipes with string tied to it, put it through your duct, then tie a rope to the string, then use rope to pull in earth cable.....job done;)
I have a method for solving this problem, I've used it a few times now. It involves a Henry, a ball of string and a couple of Tesco bags. Give it a go :)
 
thanks for comments guys , i need all phases as massive house with a lift and various kitchens with big appliances etc , but i guess the main switch being 300ma rcd then me using 30ma rcbo units is the way , there is a 6 inch duct howeve its not a straight route and they didnt pull in a draw wire just the cable (bless them )
Unless the RCBO's are double pole or single pole switched neutral then you don't want an upfront time delayed RCD. In your situation I would do as @westward10 says and use the PME for the distribution circuit, Ditch it at load end and make the house TT. Adequately support the tails so there is zero chance of them moving etc and use a four pole main switch incommer kit and RCBO's.
 
I would plonk for a ferret to solve the problem
Tie a rabbit to the far end with his but in the pipe :) release the ferret with the string tied to him.
Give him a blast from a heat gun up his rear end to get him going,when the rabbit lets out a terrifying yelp you know you got a ferret hanging on to the rabbits arse
remove rabbit and lever the ferrets teeth out of the rabbits rear and away to go
 
PME earth when taken outside of equipotential zone of origin has to be equal to supply conductors. Steel Wire Armour simply doesn’t cut it as a reliable earth. So totally agree use SWA to protect the feeder cable glanded and terminated to DNO earth. I would be tempted to run it through a 300mA time delayed rcd as mentioned above. Install it in insulated enslosure at house with a TT rod or 2 and have every circuit on 30mA rcbo’s. It’s your only option other than digging it up and installing separate earth.
 
PME earth when taken outside of equipotential zone of origin has to be equal to supply conductors. Steel Wire Armour simply doesn’t cut it as a reliable earth. So totally agree use SWA to protect the feeder cable glanded and terminated to DNO earth. I would be tempted to run it through a 300mA time delayed rcd as mentioned above. Install it in insulated enslosure at house with a TT rod or 2 and have every circuit on 30mA rcbo’s. It’s your only option other than digging it up and installing separate earth.
Where did you get that it has to be equal to the supply conductors from? Why doesn't armour "cut it" as a reliable earth? So what happens to the 300mA time delayed RCD in the event of a neutral-earth fault on one of the final circuts protected by an RCBO?
 
just rang the NICEIC help desk as needed to go definitive (lol) apparently the 35mm 4 core swa steel is 84mm which works out more than the minimum of 10mm earth that is required for bonding conductors
so looks like mr KEV 1 N is correct ......... Hail sir Kev 1 N
 
just rang the NICEIC help desk as needed to go definitive (lol) apparently the 35mm 4 core swa steel is 84mm which works out more than the minimum of 10mm earth that is required for bonding conductors
so looks like mr KEV 1 N is correct ......... Hail sir Kev 1 N
That is incorrect, 50.0 four core is the minimum size which will support 10.0 bonding.
 
just rang the NICEIC help desk as needed to go definitive (lol) apparently the 35mm 4 core swa steel is 84mm which works out more than the minimum of 10mm earth that is required for bonding conductors
so looks like mr KEV 1 N is correct ......... Hail sir Kev 1 N
Not that I'd ever say that Help Desk was anything other than 100% correct, but the current GN8 lists it as 78mm (p169). Anyway, it's very close :)
 
everything is possible , unless its not lol , I'm going to check when back on site next week to begin 2nd fix , but fairly happy with the 84mm route , however interested in the loop test result at the db so going to make it the 1st install
 
A lot of great answers here. It might be a good idea to speak to the DNO and explain the situation. While the true answer seems obvious, it's still worth talking to the DNO even if it's just to update their records.
 
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.

That doesn’t sound like a PME supply, so the requirements for bonding conductors in that situation are likely to be different.
 
Looking at the size of the job, get it dug up and done properly.
Builder's fault...he carries the can.
See the original post "as I directed" if the OP has instructed the builder what to install, I can't in all honesty see how it would be the buider's fault, the OP told the builder what to do, so down to the OP imo.
 
See the original post "as I directed" if the OP has instructed the builder what to install, I can't in all honesty see how it would be the buider's fault, the OP told the builder what to do, so down to the OP imo.
''the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth''.
Are we getting the full facts, Pete?
 
''the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth''.
Are we getting the full facts, Pete?
True, good point, did matey mention the 16mm2 earth? only he can tell so come on OP spill the beans, did you or didn't you instruct the builder to install the earth wire?
 
yep, however they supplied the cable , my input was instruction only, so as long as it is correct to the regs I'm now happy
Agree, but what were your instructions exactly? did you tell them to run the SWA and an earth cable?
 

Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock