i actually had no idea they was going to run the cable when we wasn't on site , i just gave them the list to get on site , other than that the removed and replaced a large section of the block paving and slabs
they did well considering how busy that part of the job , just a shame they didn't get it completely right lol
 
i actually had no idea they was going to run the cable when we wasn't on site , i just gave them the list to get on site , other than that the removed and replaced a large section of the block paving and slabs
they did well considering how busy that part of the job , just a shame they didn't get it completely right lol

So its not their fault then..................
 
so if i tell you that we need a 35mm swa and a 16mm earth run in for the mains , and you only run a 35mm swa and forget the earth even though theres an email trail then I'm guessing its your fault ...... or is it just me
 
so if i tell you that we need a 35mm swa and a 16mm earth run in for the mains , and you only run a 35mm swa and forget the earth even though theres an email trail then I'm guessing its your fault ...... or is it just me

So what exactly did the email say?

You previously said you gave them a list of what to get onsite ....

My experience of builders leaves me in no doubt, spell it out AND check they understand - and sometimes it'll still go wrong - the only way to avoid issues like this is to supervise/help on the day.
 
i think i started my original question by stating that the builder forgot to run the earth cable , trying to gage a easy result in solving the issue, be it by earth rod or if the builder needs to dig up the road/ earth again.
the builder him-self was the one on my last site visit to show me that his men forgot to run the earth , i confirmed to him ill do some homework and see if its a big issue or if theres an easier route

didn't realise idd have to remember word for word of emails (i do a few ) to provide as evidence ????

and the fact they undertook the works between us on site (1st fix that took 3 to 4 weeks) and our planed return to site to start 2nd fix is just unlucky but i guess worked with there plans

moving on , its now proven that the swa braid is correct for the required bonding earth size so all and all no issues

no blame needed, was about solving an issue , which has been sorted :)
 
If your protective bonding conductors require to be sized 10mm copper minimum then if you intend to utilise the armouring of the swa then the sizing must be equivalent of 10mm copper as an example an 85mm steel conductor would meet this requirement as the copper to steel ratio would be 8.5 as referenced in GN8
 
I would like to know where the NICEIC got 84mm from as this goes against GN8 which quotes 79mm and from manufacturers spec I have looked at none are quoted at 84mm.
 
Have you got it in writing from the NICEIC Helpline that the SWA is adequate for bonding?

Are they also prepared to stand over their calcs if the s**t hits the fan?
 
found this online
Screen Shot 2017-11-19 at 20.14.26.png
 
My GN8 lists 4x35mm swa cable as having 78mm of steel, which is close but no banana. It may be your particular cable has more steel or a better conductivity than average, so it might be worth checking with manufacturer's data for that specific cable?
 
1) I agree with the early post - never trust a third party with this aspect of the installation. It doesn't matter how good we are as installers if the supply is f****d.
2) I'd be inclined (if there really is no possibility of adding an additional Main earth to take advantage of the PME conditions available) to do as Westward10 suggests.
3) If, however the ferret/ terrier/apprentice can be trained to do their duty and get the extra cable installed then surely 16mmsq.csa isn't big enough anyway?
 
It seems you may be able to get away with using the armouring as your earth conductor, however I don't mean to put doubt (or possibly more doubt:eek:) but if the outer plastic sheath has any damage (from sharp stones) moisture may get in and over time and rust, so the conductivity will be reduced. Did the builder lay the cable in a bed of sand, or just back fill with what they dug out?
 

Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock