Getting back to the original point. It is bad practice to design an installation in which any component is operated above its rating. If we know that a particular double socket outlet is rated for 20A total shared between the two outlets, and we install it for the specific purpose of two appliances that we know are likely to total more than 20A for a duration in the same order as the thermal time constant of the socket parts, then that has to be bad design. In practice it is so unlikely to cause a problem, that we can probably discount it. And if we didn't know the total load, we wouldn't have asked the question in the first place.

Being pragmatic, with typical workmanship these days the fewer points the better, as the connections to the circuit cables are likely to be a weaker link than the copper busbars inside the accessories.
 
I had same situation recently where customer wanted power for washer and dryer. She stated she used them regularly at same time. I put in dedicated 32amp circuit feeding dual pattress with 2 x 1g sockets for the exact reason of 20amp rating on a 2g socket. Always better to side with caution.
 
. . . . and you cannot, if intending to, allow separate DP isolation with a double outlet but you can with a dual pattress and switched or unswitched single outlets.
 
Probably more single pole switching than double pole on socket outlets. You have to determine to get DP when choosing because either is available.
@spinlondon I was referring to above counter 20a DP isolation with 2 feeds to a dual pattress in order to isolate separately which cannot be done with one feed to a double outlet.
 

Reply to 2 singles or a double in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top