Currently reading:
Bedroom lights without earths

Discuss Bedroom lights without earths in the UK Electrical Forum area at ElectriciansForums.net

Car123

DIY
Reaction score
17
Here is another question. In my bedrooms 1 light is earthed and two are not. The lights are pendants..All plastic fittings. I have been told there needs to be further investigation. The investigation apparently needing to get up in to the loft to look for the earth. This is a problem for me as the loft is looked and choker block with my stuff. Loads of it. The loft is locked and I am not sure where the key is. (Lockdown intervened(.Anyhow I have asked the electricians why they need to investigate further. I said I thought it was okay that bedroom lights are not earthed with plastic fittings. They just dont answer. I am feeling a bit desparate about it as I have 28 days to complete the work
 
If it were not for the problem with accessing the loft I would not be hesitating. What difference does it make that one light has a CPC? This what I have wondered about? Would it be better if there were none?
The problem is we don’t know what “no earth” actually means without seeing the report or the property.

It could be that a CPC is only physically present at one fitting, which is confusing and requires investigation to find out why. Older properties may only have 2-core to all the light fittings and switches and that is sometimes ok but with a strong recommendation to upgrade.

Or it could be that a CPC is physically present at all light fittings, but not continuous between them. This is much more serious as it implies a break or degradation in the wiring somewhere, possibly rodent damage or a poorly made joint somewhere.That needs further investigation and must be resolved.

Or the wiring could leave the DB in 2-core, turn into 3-core at one fitting and then back to 2-core at the others. Which again implies a joint somewhere, and maybe not a great one at that. Further investigation needed.
 
The problem is we don’t know what “no earth” actually means without seeing the report or the property.

It could be that a CPC is only physically present at one fitting, which is confusing and requires investigation to find out why. Older properties may only have 2-core to all the light fittings and switches and that is sometimes ok but with a strong recommendation to upgrade.

Or it could be that a CPC is physically present at all light fittings, but not continuous between them. This is much more serious as it implies a break or degradation in the wiring somewhere, possibly rodent damage or a poorly made joint somewhere.That needs further investigation and must be resolved.

Or the wiring could leave the DB in 2-core, turn into 3-core at one fitting and then back to 2-core at the others. Which again implies a joint somewhere, and maybe not a great one at that. Further investigation needed.
Thanks for this. I am understanding it better now. I don't think there has been
 
What you also need to realise is coding is done at the discretion of the inspector so just because the majority on here may say C3 for no cpc with plastic class2 fitting......another inspector who to be fair is actually on site and can see/test the installation may decide it’s a c2 and that’s what your report will reflect.....possibly maybe if you ever see it ?
 
Thanks for this. I am understanding it better now. I don't think there has been

What you also need to realise is coding is done at the discretion of the inspector so just because the majority on here may say C3 for no cpc with plastic class2 fitting......another inspector who to be fair is actually on site and can see/test the installation may decide it’s a c2 and that’s what your report will reflect.....possibly maybe if you ever see it ?
Yeah I understand. I think they are a bit over the top. They were also going on about some fuse being a different make and were going to make it C2 but in the end made it C3. I am more worried now about the dead bodies they are going to find in the loft.??
 
They were also going on about some fuse being a different make and were going to make it C2 but in the end made it C3.
Manufacturers generally only test and rate their CU’s containing their own equipment, so the regs are fairly clear that mixing manufacturers is a no no.

Although the devices all have to conform to a BSEN standard there’s no universal standard for the CU enclosure itself or the bus bar connections. That means there are many different sizes and orientations of bus bars, and there’s no guarantee that a Schneider MCB will properly connect to or sit properly inside a Hager CU for example.

Mixed manufacturers is nearly always a C3 to me. If the MCB isn’t sitting properly on the bus bar and/or there are signs of thermal or mechanical damage then it’s at least a C2, maybe even a C1 if the damage is very severe.

As has been said many times, without seeing the reports or the property it’s very difficult to comment and regardless the coding of the inspector is entirely subjective. A C3 to me is someone else’s C2 and vice versa.
 
No lights need an Earth if double insulated.....right up until the 18th When all circuits need rcd protection in a domestic setting...which can’t happen with no cpc, I would say that if the others have cpcs you may have them there and they’ve just been cut out (not uncommon) which is why they’ll want to access the loft to rectify.....in fairness to the sparks if they can find it that’s a cheap fix for you
I am also confused by this. Plastic doesn't conduct so what difference would having an earth attached to a plastic fitting make? If it's not RCD'd without one then it shouldn't be RCD'd with one either? I'm sure this is wrong but would be grateful if you could explain :)
 
I am also confused by this. Plastic doesn't conduct so what difference would having an earth attached to a plastic fitting make? If it's not RCD'd without one then it shouldn't be RCD'd with one either? I'm sure this is wrong but would be grateful if you could explain :)
Ignoring the RCD issue, look at this way.

Your earth fault loop impedance (Zs) has to meet a certain value for your protective devices to operate. You need to measure and record this both on initial verification and on periodic inspection. You can do this either by direct measurement or by calculation (Ze + (R1+R2)).

How do you measure or calculate the Zs value for a circuit without a CPC? You can’t really, you need to measure R1+R2 at the very least and you don’t have an R2 to measure if there’s no CPC.

On periodics you can check earth continuity by measuring R2 at each point, but again you can’t do that if there isn’t a CPC present in the first place.

That’s why the regs say a CPC must be present at all accessories and other points on the fixed wiring even if the accessory doesn’t require an earth functionally or otherwise (double insulated).
 
Manufacturers generally only test and rate their CU’s containing their own equipment, so the regs are fairly clear that mixing manufacturers is a no no.

Although the devices all have to conform to a BSEN standard there’s no universal standard for the CU enclosure itself or the bus bar connections. That means there are many different sizes and orientations of bus bars, and there’s no guarantee that a Schneider MCB will properly connect to or sit properly inside a Hager CU for example.

Mixed manufacturers is nearly always a C3 to me. If the MCB isn’t sitting properly on the bus bar and/or there are signs of thermal or mechanical damage then it’s at least a C2, maybe even a C1 if the damage is very severe.

As has been said many times, without seeing the reports or the property it’s very difficult to comment and

Ignoring the RCD issue, look at this way.

Your earth fault loop impedance (Zs) has to meet a certain value for your protective devices to operate. You need to measure and record this both on initial verification and on periodic inspection. You can do this either by direct measurement or by calculation (Ze + (R1+R2)).

How do you measure or calculate the Zs value for a circuit without a CPC? You can’t really, you need to measure R1+R2 at the very least and you don’t have an R2 to measure if there’s no CPC.

On periodics you can check earth continuity by measuring R2 at each point, but again you can’t do that if there isn’t a CPC present in the first place.

That’s why the regs say a CPC must be present at all accessories and other points on the fixed wiring even if the accessory doesn’t require an earth functionally or otherwise (double insulated).
That's a good explanation. I think I am beginning to understand. Was this the case in 2014?
 
It looks like you are going to have to bite the bullet and move the crap in the loft space . A rental property needs to be compliant and I wouldnt be happy having the landlords gear stashed in the space I am renting - who's to say it's not a fire risk !
 
2014 EICR
It looks like you are going to have to bite the bullet and move the crap in the loft space . A rental property needs to be compliant and I wouldnt be happy having the landlords gear stashed in the space I am renting - who's to say it's not a

It looks like you are going to have to bite the bullet and move the crap in the loft space . A rental property needs to be compliant and I wouldnt be happy having the landlords gear stashed in the space I am renting - who's to say it's not a fire risk !
I cannot assure you that my rental property is fully compliantt. The tenant is perfectly happy with the house. He writes that he loves it there and one reason is that I am a good landlord. Anyhow snarky it turns out that the electricians now say that it can remain as it is and they just need to put a label on the consumer unit. They seem to have concluded this after I requested more understanding of the matter. Thank you to all the people on here who have offered advice and help. I did try and upload the 2014 but it would not attach..
 
Ignoring the RCD issue, look at this way.

Your earth fault loop impedance (Zs) has to meet a certain value for your protective devices to operate. You need to measure and record this both on initial verification and on periodic inspection. You can do this either by direct measurement or by calculation (Ze + (R1+R2)).

How do you measure or calculate the Zs value for a circuit without a CPC? You can’t really, you need to measure R1+R2 at the very least and you don’t have an R2 to measure if there’s no CPC.

On periodics you can check earth continuity by measuring R2 at each point, but again you can’t do that if there isn’t a CPC present in the first place.

That’s why the regs say a CPC must be present at all accessories and other points on the fixed wiring even if the accessory doesn’t require an earth functionally or otherwise (double insulated).
The electricians have now concluded that it can stay as it is. Interesting. Thanks for your advice
 
I reckon your stuck on this one mate, if there’s no cpc then it’s not rcd’d so depending on inspector you are probably getting a C2 regardless...so it’ll need sorting and that will involve accessing the loft
Thanks for your advice. I feel a lot more informed. But guess what the electricians have concluded that it's fine to leave it and stick a lable on the consumer unit. Funny that. This came after I asked for clarification from them. I explained that I was stupid and apologised, one week later to the day they concluded it was alright as it is. ?
 

Reply to Bedroom lights without earths in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top