Yes, you're correct if fire got into that partition it would be an issue.

A hole that was cut much bigger than was needed.
No it wouldn't be as there should be cavity barriers. The size of entry shouldn't be relevant as there will always be passage around the cables regardless of size.
 
No it wouldn't be as there should be cavity barriers. The size of entry shouldn't be relevant as there will always be passage around the cables regardless of size.

I could be wrong, and will happily stand corrected, but doesn't BS7671 make reference to holes in a domestic DB solely with regard to finger access in front, bottom or sides and holes larger than 1mm on top, with no reference made about rear?
 
I could be wrong, and will happily stand corrected, but doesn't BS7671 make reference to holes in a domestic DB solely with regard to finger access in front, bottom or sides and holes larger than 1mm on top, with no reference made about rear?
No reference is made regarding the rear.
 
I might be wrong, but when 421.1.201 first came out in the BYB, it was about removing the source of fuel for a fire, and nothing to do with containment of a fire.

Has this recently changed?
 
I might be wrong, but when 421.1.201 first came out in the BYB, it was about removing the source of fuel for a fire, and nothing to do with containment of a fire.

Has this recently changed?
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames.


It is important for the installer to seal all openings into the enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables - see Figure 6. The intent of the sealing is to ensure that, as far as is reasonably practicable, any fire is contained within the enclosure or cabinet and the escape of flames to the surroundings of the cabinet or enclosure or into conduits trunking or ducting is minimised, as intended by Regulation 421.1.201.

Good workmanship and proper materials must be used, and account must be taken of the manufacturer’s relevant instructions if any.
 
The intent of Regulation 421.1.201 is considered to be, as far as is reasonably practicable, to contain any fire within the enclosure or cabinet and to minimise the escape of flames.


It is important for the installer to seal all openings into the enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables - see Figure 6. The intent of the sealing is to ensure that, as far as is reasonably practicable, any fire is contained within the enclosure or cabinet and the escape of flames to the surroundings of the cabinet or enclosure or into conduits trunking or ducting is minimised, as intended by Regulation 421.1.201.

Good workmanship and proper materials must be used, and account must be taken of the manufacturer’s relevant instructions if any.
At no point does that Reguation infer to containing a fire.
 
Just for information not massively known is that Fire Proof Filing Cabinets are not fire proof if not locked, the expanding air in the event of a fire will open the drawers.
 
New posts

Reply to The Future of Fuse boards...? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top