Has anyone come across surge protection devices being the source of an RCD trip at consumer unit ?
 
not particularly

but apparently they can be a nuisance-downstream of rcds

what type of SPD? if it's a multilead spd -can you swop it out to confirm?

if it's in the DB i assume it should be 'upstream'
 
Last edited by a moderator:
Yep...known them to cause or at least contribute to nuisance tripping, mainly when several SP leads are in use on a system with a 30ma RCD main switch ,after removal (of the leads)things improved somewhat,and no other obvious causes found.
They are often the cause of low IR readings if you miss them,typically around 0.3Mohm.
 
yes I have a couple of years ago it seems they can cause nuisence tripping, but I had one for my computer and I did not have any problems so I cannot say for sure.
 
Surge protection devices do trip RCDs as they regulate transient voltages and RCDs are voltage sensative.

The class I SPD device is normally the one fitted at the origin of the installtion and is for protection against direct lightning strikes.

Class II are normally at sub board level and used for transient voltage surges on indirect lightning strikes, motors flourescent fittings, and equipment that have transient switching loads.

Class III are the very local ones used at individual pieces of equipment or on extension leads.

Most installtions that require SPD use a combination of devices and they are mostly class I and II which would be upstram of RCD protection.

Unfortunately what happens with the class III in the UK is when you get brown outs, or even switching on the distribution network it will cause the SPD to intiate and of course it will unbalance the RCD causing it to trip
 
Surge protection devices do trip RCDs as they regulate transient voltages and RCDs are voltage sensative.

The class I SPD device is normally the one fitted at the origin of the installtion and is for protection against direct lightning strikes.

Class II are normally at sub board level and used for transient voltage surges on indirect lightning strikes, motors flourescent fittings, and equipment that have transient switching loads.

Class III are the very local ones used at individual pieces of equipment or on extension leads.

Most installtions that require SPD use a combination of devices and they are mostly class I and II which would be upstram of RCD protection.

Unfortunately what happens with the class III in the UK is when you get brown outs, or even switching on the distribution network it will cause the SPD to intiate and of course it will unbalance the RCD causing it to trip

What is a "brown out"?:confused:
 
Surge protection devices do trip RCDs as they regulate transient voltages and RCDs are voltage sensative.

The class I SPD device is normally the one fitted at the origin of the installtion and is for protection against direct lightning strikes.

Class II are normally at sub board level and used for transient voltage surges on indirect lightning strikes, motors flourescent fittings, and equipment that have transient switching loads.

Class III are the very local ones used at individual pieces of equipment or on extension leads.

Most installtions that require SPD use a combination of devices and they are mostly class I and II which would be upstram of RCD protection.

Unfortunately what happens with the class III in the UK is when you get brown outs, or even switching on the distribution network it will cause the SPD to intiate and of course it will unbalance the RCD causing it to trip

Malcolm,
No SPD will protect against a direct strike, they are not designed to protect against direct strikes, even origin spurge protective devices are only designed to protect against man made and naturally induced transients to a level well below the energy of a direct strike.

HTH.
 
Malcolm,
No SPD will protect against a direct strike, they are not designed to protect against direct strikes, even origin spurge protective devices are only designed to protect against man made and naturally induced transients to a level well below the energy of a direct strike.

HTH.

Their are Transient protectors specifically design to protect against Lightning transients.

Regards Chris
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD Tripping and Surge protection devices
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
SIMBO,
Last reply from
MarkieSparkie,
Replies
10
Views
17,733

Advert

Back
Top