Currently reading:
9.5 kw shower on 6mm ?
Discuss 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net
just been to a job , saw that the shower 9.5 kw is on 6mm t&e the cable goes in the wall and under floor boards ,No insulation, to the board (A cable run of no more than 10 m) . I said downgrade the shower to 8.5 max. Is it really necessary ? never quite sure , its borderline to me .
I also doubt that they will be having the shower running at full whack, not unless they have skin like leather.
Honestly don't understand these shower unit being 9.5 TO 10.5KW, The shower unit that i currently have in China is 4.2 or 4.6KW (do they do this sort of rating size in the UK??) and i can't have the thermostat turned up more than half way.
So what's the story with these Mega Watt shower units that seem to abound in the UK?? ...lol!!!
The shower is either "on" or "off", and therefore always at full wack electrically. The temperature is adjusted by varying the flow. Granted, most showers have an "economy" setting which is normally half-power, but I don't know anyone who uses this unless it is a very hot summer day.
7.5 kw is the smallest UK size (formerly 7.2 kw) and on a normal British day it delivers something between a trickle and a sprinkle :)
Never having had or wanted an electric shower in the UK, i can't say how they operate. What i can say is that the unit i have, has a thermostat controlled element. It doesn't however have an economy setting. The water flow is either on or off, it's not exactly (or anywhere near a power shower levels) powerful, but more than adequate for a decent shower.... lol!!!
Would anyone in the UK use an electric shower, if and when they have gas/oil central heating systems or is it just those without a gas supply etc???
I have an oil-fired combi-boiler and it supplies all our hot water, including to a very nice mains thermostatically controlled shower. However, as we have had a few problems with our very old boiler over the last few years I decided to fit an electric shower as a backup in the kids' bathroom. It is only 7.5 kw, and the flowrate is very poor, but it is adequate. Plus, it saves me money :)
just because it's bigger than next door's. same with cookers. next door's just had a 10kW unit, so we must have a 12kW. one.
In this situation all you can do is present the client with the facts and explain that if a new installation were to be added today then the way it is wired currently would not be acceptable.
This is where a clamp meter is worth it's weight in gold as you can prove to the client what current is being drawn. It doesn't take a mathematician to evaluate the results recorded on the meter.
I personally would sow the seed for installing a new 10mm radial circuit and make the client fully aware that there is the possibility that the shower as it is may become a nuisance if the shower is used for a longer period of time BUT it's THEIR decision.
I live in a property where the shower would trip the MCB which meant having to wipe bubbles from my eyes, get out and go down to reset. The problem was though as the MCB had got to a certain temperature it would take about 10 minutes to reset. Once reset there was normally just about enough time to get rinsed off and get out. The worst time was I was sat next to the CU trying to reset because the wife had been washing her hair, trip, trip, trip, trip, trip..... Haven't you done it yet? Trip, trip lol
Eventually I replaced the board and used 60898 mcb's and never had a problem since, everything the same apart from the breaker (Old 30A mcb replaced with to a 32A EN60898 on 6mm cable)
As mentioned though, So long as the MCB is rated lower than the maximum current carrying capacity of the cable (taking into consideration any influences such as insulation) then the only bother is the inconvenience. The protective device is only doing exactly what it is designed to do therefore eliminating any risk to the user - Well, unless they drip water all of the mcb/CU when trying to reset? lol
what's wrong with a watering can on a pivot, pulled with wet string (10mm wet string, of course)
I have a feeling you will be told, "well it has worked like this for ages, and we have never had a problem!"
To give yourself piece of mind, just do a full cable calculation and find out what the current carrying capacity of the cable is. In most installations i have found Insulation (Ci) and cable grouping (Cg) at least affect the cable capacity. These figures often make the current carrying capacity requirement much higher than that offered by a 6mm cable.
Depends on how precise you want to be! I have only seen a couple of heat damaged 6mm cables in my time caused by overloading. One was very bad at the consumer unit - a house full of females - shower on A LOT and for long periods.
I always go on the side of caution to cover my ---. So would always point out issue and recommend a downgrade of shower or upgrade of cable! Up to the customer then and you can sleep at night!
i think thats right, its bang on the limit. but i would be ok with it if it seems to be holding up. keep it on the 40 and tell them they are pushing there luck. whatever happend to the super 7 shower ??? 10.5 kw crazy !!!
And the other little addition is, it may well be on the limit on a 40A, but 1.13 x 40 is over 45A......
I've seen a 6mm2 cable melting on a 10.8kW shower, again as prev poster mentions where it connects at the neutral bar. Always wonder if it was a loose conn (can't tell when all melted).
Yeah but doesn't China run at 650 Volts :chinese:
I see the good old 9.5kw shower on 6mm conundrum is still rumbling on after 4 pages lol.
Not in the least bit surprised
Anyways im off for a shower now , 8.5kw wired in 4mm if anyones interested.
If im not back assume the worst
It's no good people shouting about how a cable should be ok because the shower "should" only on for 10 mins. It's either suitable for the OCPD or it's not for goodness sake.
Really can't see what the argument is.
I was always of the understanding, the higher the kw rating of the shower, doesn't mean it gets hotter, just allows more water to flow at the required temperature.
The lower the power rating the less amount of energy it has to heat the water so it flows slower to maintain the temperature.
remember a few years back one of the sheds was doing 10.5kw showers for about £45 well a bloke fitted one on 6mm replacing his old 7.5kw cable ran on outside wall of house and it melted it from one end to the other,guy was well peed off.asked for a price and said the cost of cable alone was more than cost of shower,got quite funny about it so I told him that my shower worked fine so either way it didnt bother me if he had it fixed or not.lol
Nice answer haha. Not your fault his DIY went belly up!
Indeed mate, higher rating means better flow as power is fixed and temp is controlled by throttling water flow. Downside of a lower rated shower is on a winters morning when the water entering the unit isn't much above freezing... :christmaswindow:
Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net