B. Gas decided to a. relocate a customers meter and b. connect it to the gas main in plastic. The old meter was removed leaving a stub of pipe with the MPBC still connected. My view is that this is now an earth rod, auxiliary to the distributor earthing conductor.. Another guy looked at it and said its still good for MPBC.
It's a PME supply with good Ze.
Settle a debate please....
 
Some say, that if it can still introduce a potential into the property then it should be bonded. as extraneous
 
Apologies, more info. The stub is about 150mm and located in a to be boxed in area under the stairs. It's going to be impractical to confirm its continuity in future when the builder has finished
 
I believe you have to make the call, is it extraneous metal work? others when they get home from work may have a differing opinion, sorry I can't be of more help, how difficult would it be to bond it?
 
if it's extraneous, entering the building, then the bond to it is a main bonding conductor. end of.
 
If it was extraneous before the meter was moved, then it's still going to be extraneous NOW!!

If the pipe has been totally isolated from any gas supply both inside and outside, it could well also act as a local earth rod (if it has a Ra value in single figures) that can be used to reinforce the DNO PME's supply. Either way it needs to be connected to the installations MET ...and as Tel stated, with a 10mm conductor
 
but if isolated from incoming gas supply, and acting as an earth rod, then the cable to it would be an earthing conductor, not a bonding conductor.:rofl:
 
and B Gas input following ages being passed around and on hold? " get your angle grinder and the pipe off at floor level, it's not connected to our network"
 
And if the pipe is painted then ask uksparks to come and sort it out for you he's a dab hand at them . :rofl:
 
I found the original redundant steel gas pipe that had fed my house. Didn’t take me long to weld a stud to it and connect it to the earth nest. I was on a TT supply back then.

Don’t ask me why. A steel gas pipe makes nearly always makes a better earth than the old lead water pipes.

At work I had 4 x 8” welded steel ducts laid under a double rail track and two heavy haulage roads about 200’ in length each. Each had a stud welded at each end. One end was connected to the substation MET the other end to the switch room transformer bays MET.
My philosophy is if it’s conductive and it’s in the ground, use it.

PS I’ve only worked on private MV networks so don’t start quoting BS7671.
 

Reply to Is it still a Main Protective Bonding Conductor? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top