Hello all, excuse my bad grammar spelling etc. today i had the people from building control around to sign of my cu change
at my house,here is my question. My mum had her oven changed a little while ago and it has a design current of around 10.5 amps, the old fuse protecting was a 40 amp wired in a 10mm t+e, i have since replaced this with a 16 amp breaker and put connecters at old cooker switch and a blank plate. I done this as section h of osg states you can do this and dont need a switch if the circuit breaker is to be used as one. The inspector told me this is not Good and my interpretation is wrong. And i need a local isolation switch. I want to know what others opinion was on this he also said the oven is not fixed equipment? If im wrong fine but how do i remedy the situation its a double box do i just put the old cooker switch back on. I did do a little search before posting but could not really find what i was looking for. Any advice greatly appreciated!
 
And another reason i queried is that an electrician that i worked with done a kitchen extension and all appliances were done this way, but the fuse box for extension was actually in the kitchen, is this more acceptable or still not good practice?
 
it's always good practice to provide double pole isolation for any item of fixed equipment. as murdoch said. an earth fault will take out an RCD, so isolation of both L and N is recommended.
 
And another reason i queried is that an electrician that i worked with done a kitchen extension and all appliances were done this way, but the fuse box for extension was actually in the kitchen, is this more acceptable or still not good practice?

Hi Julian,

I've looked at many threads on local isolation and functional switching etc etc and there seems to be differing views, but the main theme seems to be that it is pretty bad practice not to provide local ioslation and in your case it probably doesn't comply with BS7671 (see below) because a MCB is not DP:

Page 45 OSG (ii)
ISOLATION
"The device must switch all live conductors in a TT system and all line conductors in a TN system."

Probably best just to put the 45A DP cooker switch back on :wink_smile:
 
it's not just that, happy. if the cooker had a N-E fault tripping the rCD, it's much easier to isolate the cooker with a D/P switch than leave a RCD that might also supply sockets and lights off till a spark can attend.
 
I've looked at many threads on local isolation and functional switching etc etc and there seems to be differing views, but the main theme seems to be that it is pretty bad practice not to provide local ioslation
The switch is not required for isolation.
It depends whether you think emergency switching is required for an oven.

and in your case it probably doesn't comply with BS7671 (see below) because a MCB is not DP:Page 45 OSG (ii)
ISOLATION
"The device must switch all live conductors in a TT system and all line conductors in a TN system."
OK for TN, then. MCB, that is. Section 537 & Table 53.4.

Probably best just to put the 45A DP cooker switch back on :wink_smile:
Yep.

Why do people keep quoting the OSG instead of the actual regulations?
 
Hi Julian,

I've looked at many threads on local isolation and functional switching etc etc and there seems to be differing views, but the main theme seems to be that it is pretty bad practice not to provide local ioslation and in your case it probably doesn't comply with BS7671 (see below) because a MCB is not DP:

Page 45 OSG (ii)
ISOLATION
"The device must switch all live conductors in a TT system and all line conductors in a TN system."

Probably best just to put the 45A DP cooker switch back on :wink_smile:


Thanks all for replies nails are in the coffin
 
And another reason i queried is that an electrician that i worked with done a kitchen extension and all appliances were done this way, but the fuse box for extension was actually in the kitchen, is this more acceptable or still not good practice?

probably rcbo's? but my limited knowledge is in line (no pun intended) with other replies.
 
now..

i`v seen this in renteds...where the only means of isolation for the cooker has been the MCB..

i thought it was crap then and i think its crap now....

this kind of install is only performed by them offering the cheapest of cheapest quotes...in fact in my mind it aught to be made a requirement to have a means of local isolation for such equipment...as on the 2 previous occasions where i have come across this..the dis-board was in the cellar below the kitchen area...

really poor...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16amp b type breaker for oven.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
julianacb,
Last reply from
GLENNSPARK,
Replies
31
Views
4,675

Advert

Back
Top