Solarspark
Hi all .First post .
I'm an electrician working for a solar company company.
We have a commercial solar install starting tomorrow.
The array is split into three lots of 33kw . I can't be certain on very more details than that for the time being.
It will have 3 single phase inverters but be fed via a three phase supply. My boss wants to meter it at the switch room db. (origin of supply) . Then split the phases at the location of the inverters via a connection box and not use a DB.
Is it me or is he out of his tree ? I full intend to force him to consult the niceic over this. But I would very much like to confidently tell him that he is a numpty when I see him in the morning .
Shirley he either needs to install a DB at the inverter location or run three separate circuits from the origin of supply ?
What do you guys think ?
Out of his tree.
So this is a 100kW installation and he doesn't want protection on the circuits.....
Non compliant on too many fronts.
Or do you mean 3 x 3.3kW? You can create your own db from a single phase board with a 4 pole main switch and three mcbs one for each circuit. As you know, each circuit must be protected, so that it would be just as cost effective to buy a small 3 phase board.
Putting the meter in the switchroom is OK, however depending upon the distance, it may be better to meter nearer the inverter (get paid for the losses :) )
You say you are an electrician, just check BS7671 no need to consult the NICEIC...
3phase supply to 3 single phase solar inverters
Solarspark,
Gary K,