Hi all, (not the standard domestic setup for me)

-3 phase overhead supply TT. coming in via 3 200amp fuses (not sure what type so unsure what to write on cert) any ideas?

-Then goes to large rusty switchfuse (see pic). Bs3185?? Earthing conductor straight into concrete.

-Fairly large swa cable (not sure on size)(any ideas?) from here to 3phase board about 100mtrs away which also feeds swimming pool etc.

I want to install some lighting from this board.

My questions:
1. what r the supply fuses?
2. Testing ze at switchfuse (do I just remove the top brown guard?) or just settle with zs at board down stream.
3.whatsize is the 4 core swa (cpc is the armour)
4. what size is the earthing conductor (shall i calculate by measuring and applying pi etc


-thanks
 
Last edited:
You maybe need to firstly upload the photos, and secondly learn how to know the size of a cable by looking at it.

Then go and do a the C&G 2394 and 2395, that will help you learn about testing procedures, a copy of GN3 will also be invaluable to you in the future.

I hope you are not charging anyone for this work?
 
I think that I posed something about the competence of people doing EICR's tonight, and also a few days/weeks ago.
This just seems to confirm my stance.
Now if the OP is employed then their employer is in serious breach of the EAWR, if not then the OP is.
This is just getting silly now.
 
I think that I posed something about the competence of people doing EICR's tonight, and also a few days/weeks ago.
This just seems to confirm my stance.
Now if the OP is employed then their employer is in serious breach of the EAWR, if not then the OP is.
This is just getting silly now.

One of your posts was on my question about a reg. to which you jumped the gun. But your right in this instance :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Advice needed on testing this large switchgear on TT supply (with photos)
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
bleach,
Last reply from
D Skelton,
Replies
8
Views
1,734

Advert

Back
Top