Currently reading:
Bonding to Gas and water am2

Discuss Bonding to Gas and water am2 in the The Welcome Forum area at ElectriciansForums.net

Reaction score
13
hi all,

I have my am2 coming up. Just going over a few things. I am correct in saying that the Gas bonding would terminate in to the clamp below the joint, and not above it?
Also, I was going to use one continuous length of 10mm is this allowed, or is it better practice to use to lengths?

Regards
802D7480-3C99-4BD1-A4CA-569EA86CAE79.png
 
Bond needs to be on consumer side not the meter providers side, one cable is fine if unbroken, but i would install 2 and labell them, thats personal choice
 
if the supply is from the bottom, then the clamp needs to be below the branch joint.
 
I thought he was referring to bonding the gas and water together
 
yeah i know. the idea of using a single cable, unboken, is to prevent wet-pants from dissing one service when messing about with the other.
 
Are you trying to say wet pants doesn't reconnect bonds? lol
 
Bond needs to be on consumer side not the meter providers side, one cable is fine if unbroken, but i would install 2 and label them, thats personal choice

2 cables are OK by the regs BUT best practice says a single continuous cable is better.
 
hi all,

I have my am2 coming up. Just going over a few things. I am correct in saying that the Gas bonding would terminate in to the clamp below the joint, and not above it?
Also, I was going to use one continuous length of 10mm is this allowed, or is it better practice to use to lengths?

Regards
View attachment 41146
Consumers side of the intake
2 cables are OK by the regs BUT best practice says a single continuous cable is better.
1 Bond to the H2O and 1 bond to the Gas= 2 conductors it would need to be continuous, which would be difficult if the gas and water entered the building on different sides of the building, can you show me where it says 1 conductor is best practice Murdoch please?
Sizing main protective bonding conductors - https://www.voltimum.co.uk/articles/sizing-main-protective-bonding-conductors
 
Last edited:
Can you quote the regulation number stating this please?
For the record I prefer an unbroken cable if I was only using one
Section 54
Sorry, that’s nonsense. Either individual conductors to gas and water, or one single, continuous conductor serving both.
It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.
 
Section 54

It is not nonsense, protective conductors have got to be continuous.
It is up to you if you want to use one conductor for water and another conductor for gas but continuity is key no breaks at all.
Guidance note 8 (earthing & bonding) page 57.
Thanks not got GN 8 does it say anything about seperate conductors being no compliant? because I think the post saying it is, and a single conductor is the best practice is incorrect.
 
Thanks not got GN 8 does it say anything about separate conductors being no compliant? because I think the post saying it is, and a single conductor is the best practice is incorrect.

Hit, nail and head and rather proves my point I think.

I would have thought that you would have it Pete!
 
A single conductor to each service is the ideal situation, however to use a single conductor to one service and loop it on to the next service is totally acceptable.
There is a suggestion in GN8 that a looped service should be unbroken to avoid the chance of a disconnection at the first service also causing disconnection at the second service.
Though it is interesting to note that this will only be applicable if someone carefully undoes the wiring connections, in which case they would probably be careful to reconnect, rather than just snipping the conductor.
However where the conductors are not looped there is no suggestion that they need to be unbroken and in many cases will often be jointed several times before they arrive at the MET particularly in large installations.
 
there is no reg. stating that a single bonding conductor to 2 services should be continuous. it's just been accepted as good practice for the reason i stated in post #5.
 
Right - this isn't a reg, its guidance

Most people don't have the Guidance Notes ......

If the IET intended this to be a reg it would be in the big book
You can argue as much as you want and dismiss advice here.
The op who posted wanted guidance and if he is going to sit his AM2 and does that he is going to fail.
The issue of you not having the guidance note is your problem ,you can choose to refer to as many books and notes as you wish.
The Guidance note 8 (Earthing & bonding) is an exampanded form ofchapter 54 of BS 7671 2008 amendment 3.
All information in their is correct and binding.
 

Reply to Bonding to Gas and water am2 in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock