Hi so i want to install the following over a three phase supply.

South roof - 35 degree pitch.
14x Renesola Virtus 2 250W.
One string (???)

East Roof - 35 degree pitch.
8x Renesola Virtus 2 250W
One string

Total of 5.5kW.

Inverter is to be SMA Sunny Tripower 5000TL-20
G59 installation with DNO approval.

I think this is ok but my PVSOL states 'please check the system parameters! Further calculation possible. Please observe and design recommendations made by the manufacturer.' But i'm not sure where to go from here. I think it might be showing this due to the inverter being 3phase.

Any help appreciated...

thanks
 
Just quickly checked via Sunny design (you can download it for free from SMAs website), and that all looks ok. one string each orientation as you suggested.

Also someone correct me if wrong but if you are using a three phase inverter wouldn't that 5.5kwp come under G83/2 (as you would be splitting equally over the three phases, hence well under 3.68kwp per phase and as there are no parallel strings into one input also comfortably under the 16 Amps per phase).
 
Would you not be better just keeping it <4KW and doing it on a G83 anyways. Just do the South Roof. Better FIT return probably. Your design regardind panel arrays seems ok. Max VOC on that inverter is 1000v so 14 in series (one string) is fine (523.6V, assuming JC250M Panels).
 
Just quickly checked via Sunny design (you can download it for free from SMAs website), and that all looks ok. one string each orientation as you suggested.

Also someone correct me if wrong but if you are using a three phase inverter wouldn't that 5.5kwp come under G83/2 (as you would be splitting equally over the three phases, hence well under 3.68kwp per phase and as there are no parallel strings into one input also comfortably under the 16 Amps per phase).

Missed that completely. You are dead right Tuck. 16A per phase under G83. You would only require G59 if going over 16A on a single phase.
 
Thanks guys... there is no more room on the south for more panels. I should perhaps added that this is part of a 13.5kW system. The 5.5kW as above and also 8kW on the West using SMA 8000TL Tripower. So over 3.68/ phase.

Wouldn't necessarily used SMA but they have inverters to fit the design.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
West Sussex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Can some body confirm my 3 phase PV design?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
saint,
Last reply from
jason121,
Replies
7
Views
1,873

Advert