Discuss Central heating - vaillant system boiler in the Central Heating Systems area at ElectriciansForums.net

rick

-
Arms
Reaction score
9
A plumber friend of mine has asked for some help wiring up a Vaillant Ecotec system boiler in an S plan configuration. I am familiar with S plan but can’t work out how to do it with this boiler, and the Vaillant manual whilst very good on the gas side is a bit lacking electrically…

The boiler needs L-N-E from the wiring centre, no problem. But then there are terminals 3, 4 and 5 which are labelled “external controls”. I am planning on using the Honeywell wiring centre to make things a bit easier, but unlike a standard boiler, I really can’t see how to wire this boiler up. Planning to have 2 motorised valves, programmer, cylinder stat and room stat.

Also, does the room stat need to be 24v or 230v, or either, have read conflicting things on this.

Has anyone come across similar and could give me some pointers as I am really tearing my hair out on this one!
 
Hi Rick

You can use a 24v or 230 room stat, terminals 3 and 4 should have a link attached this is the boiler control circuit, terminal 5 is a neutral connection. You connect your programmer switch connections to terminals 3 (LiveOut) and 4 (switched live) Page 29 Fig 4.15. 3 of the manual shows how to connect external controls to boiler.
Hope this helps

Danny
 
Hi Again

Forgot to say in my last post i would take supply from swich fused spur to the boiler L N E first as boiler needs permanent supply and supply your wiring centre from 3 Live out and 5 Neutral and of course and earth, then terminal 4 is the live in to the boiler. Should be simple to work out valve controls the honeywell web site has s and y plan wiring diagrams.
Danny
 
I find the honeywell ST9001S a very good match to the Vailliant ecoTEC

That depends on the application. S types are most suitable for landlords or people who like to keep a keen eye on service intervals. It is also only a one-day device. For most people I would have thought a 7 day timer such as the ST9400C would be appropriate.
 

Reply to Central heating - vaillant system boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
543
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock