Did an EICR last week, a few small things to clean up but the main thing is that 3 of the upstairs light fittings are class I metallic with no cpc/earth. Doing the remedials tomorrow and talking to another spark he says that the earth to the fittings has to be a min of 4mm csa!
Now, I've learned from a few good sparks and I've work for/and employed a few good sparks and never have I seen a 4mm earth in a domestic light fitting. Have I/we been doing it wrong for all these years? My friend makes a very good point in the regs, 543, and now I'm on the ropes trying to defend my decision to throw in a 1mm, any help on this would be appreciated because there's a couple of pints riding on this lol.
Do you or have you ever put a 4mm csa to light fittings being fed from 1.5mm twin? I never have but I may have to change my ways if this is correct.
Ps, foot note on install info:- 1970 rewire, red+black, 1.5mm cable no cpc on any of the upstairs light circuit, IR @ 11M and the customer is my neighbour and a good friend that always gets me a pint after working for him (builder), think I've covered enough info unlike others that ask for help lol.
Now, I've learned from a few good sparks and I've work for/and employed a few good sparks and never have I seen a 4mm earth in a domestic light fitting. Have I/we been doing it wrong for all these years? My friend makes a very good point in the regs, 543, and now I'm on the ropes trying to defend my decision to throw in a 1mm, any help on this would be appreciated because there's a couple of pints riding on this lol.
Do you or have you ever put a 4mm csa to light fittings being fed from 1.5mm twin? I never have but I may have to change my ways if this is correct.
Ps, foot note on install info:- 1970 rewire, red+black, 1.5mm cable no cpc on any of the upstairs light circuit, IR @ 11M and the customer is my neighbour and a good friend that always gets me a pint after working for him (builder), think I've covered enough info unlike others that ask for help lol.