Just a bit of info required , just been checking all over the house checking for a earth feed to light fittings and switches , ( a friend informed yesterday that there friend have more or less sold there house , but an electrcal inspection has come up with no cpc to all the light switches ) .
I have found 3 light switch back boxes that do not have a earth feed to them , now the question is can I fit a plastic box inplace of the metal one that is in there and not need a earth feed to them ! .
All the light fittings have a earth feed to them ! , every circuit in the house is protected by a RCD .
cheers
BB
 
it's also an earthing terminal (MET). better would be to connect to the earth bar in the CU in the correct point for the circuit. and, if not mechanically protected, should be min. 4mm, but that's a minor point.

Hi
Thanks for your reply , what would be classed has "mechanically protected" under the floor boards ! , that is were I put the 2.5mm² cpc run , crikey I would not of liked to have tried to put 4mm² to my light fittings , the ceiling would of come down with the weight of the copper lol .
anyway thanks for your reply , great place to learn .
ps: by the way when did that reg come out 543.1.1 regarding the 4mm² , will feed it into my CU , has been recomemended , where I have it fed from now is the same point my CU is fed from ! .

BB
 
Hi
Thanks for your reply , what would be classed has "mechanically protected" under the floor boards ! , that is were I put the 2.5mm² cpc run , crikey I would not of liked to have tried to put 4mm² to my light fittings , the ceiling would of come down with the weight of the copper lol .
anyway thanks for your reply , great place to learn .
ps: by the way when did that reg come out 543.1.1 regarding the 4mm² , will feed it into my CU , has been recomemended , where I have it fed from now is the same point my CU is fed from ! .

BB
2.5 protected i,e, in conduit or trunking, yes the MET is electrically connected to the earth bar in your CU but it is recommended that cpcs are connected in the CU
 
2.5 protected i,e, in conduit or trunking, yes the MET is electrically connected to the earth bar in your CU but it is recommended that cpcs are connected in the CU

Hi
Thanks again for your help , just one more and I will leave you alone , if I was to get a EICR for my house would they not pass it , if they had seen the 2.5mm2 cpc I put in the ceiling void to the lights ! .
 
2.5 protected i,e, in conduit or trunking, yes the MET is electrically connected to the earth bar in your CU but it is recommended that cpcs are connected in the CU
Hi
Thanks again for your help , just one more and I will leave you alone , if I was to get a
What size cpc and what routing did you take when installing he seperate cpc as there are regulations governing what should be done

Hi
From the MET straight up into the loft then through each floor joist to each light ! , going to put it into the CU earth bar instaed of the MET .

cheers
 
I have just found the same Reg 543.1 in my 1981 Fifteenth Edition but it has been around longer than that.
Thanks for that , looks like I am going to have to change the 2.5mm2 to 4.0mm2 to the lights mam a mia , that was a job and a half putting in the 2.5mm2 from what I can remember , but you can't have enough supplimentry bonding in the house and I have a lot , water n gas pipes were I have been able to get to them , I hink there is more copper in the cpc's around the house than in Zambia ! .

cheers guys and thank you all for your comments and help .

BB
 
Thanks for that , looks like I am going to have to change the 2.5mm2 to 4.0mm2 to the lights mam a mia , that was a job and a half putting in the 2.5mm2 from what I can remember , but you can't have enough supplimentry bonding in the house and I have a lot , water n gas pipes were I have been able to get to them , I hink there is more copper in the cpc's around the house than in Zambia ! .

cheers guys and thank you all for your comments and help .

BB
If you are going to access the routes to the lighting points why not run a new twin and cpc cable? sounds like you have been bunging supplementary bonding every where, has the pipework been tested to see if it actually requires bonding?
 
Thanks for that , looks like I am going to have to change the 2.5mm2 to 4.0mm2 to the lights mam a mia , that was a job and a half putting in the 2.5mm2 from what I can remember , but you can't have enough supplimentry bonding in the house and I have a lot , water n gas pipes were I have been able to get to them , I hink there is more copper in the cpc's around the house than in Zambia ! .

cheers guys and thank you all for your comments and help .

BB

Was all that bonding actually necessary? Bonding things which don't need it can potentially increase danger rather than reduce it.
It would be far better to rewire the circuit than run an additional cpc, the old cables are likely to be getting towards the end of their expected lifespan of they aren't past it already.

What Zs readings did you get when you tested the 2.5mm cpc?
 
Hi
Thanks for your reply, yes you are right am going to rewire all the lower floor lights and switches , to be honest I was thinking of doing just that , just needed someone to push me to do it .
Best regards
BB
 
Thanks for all your feedback again have decided to rewire the lower lights n switches , my next question is what is the recomended csa of the cable to use ! .
ie 1.omm2/1.5mm2 / 1.5mm2 for radial n 1.00mm2 to switches ! .
cheers

BB
 
Thanks for all your feedback again have decided to rewire the lower lights n switches , my next question is what is the recomended csa of the cable to use ! .
ie 1.omm2/1.5mm2 / 1.5mm2 for radial n 1.00mm2 to switches ! .
cheers

BB

The recommended size is the size which you have calculated using the information in your regulations book.
Mixing cable sizes in a simple installation is unnecessary, calculate thencable size required for the circuit and stick to that size throughout the circuit.
 
Was all that bonding actually necessary? Bonding things which don't need it can potentially increase danger rather than reduce it.
It would be far better to rewire the circuit than run an additional cpc, the old cables are likely to be getting towards the end of their expected lifespan of they aren't past it already.

What Zs readings did you get when you tested the 2.5mm cpc?

Hi
Thanks for your reply , is there a need to check the Zs when there is a RCD in the circuit ! .
BB
 
Hi
Thanks for your reply , is there a need to check the Zs when there is a RCD in the circuit ! .
BB

Yes, you need to meet the Zs requirements of the over current protective device protecting the circuit. Using the RCD for fault protection is a last resort if you can't meet the Zs requirements of said device, but in my opinion this should only be considered if you have a TT supply.
 
Hi
You must put this label on the consumer unit with the circuit details!

Screenshot_2017-05-16-20-28-38.png
 
To be fair it might just make someone think twice before fitting metal gear. I know it's unlikely, but even if it makes the difference a couple of times it's better than nothing.
 
Which regulation is that then?
If the customer doesn't want the work done then walk away from the job, simples.

It's not a regulation, as has already been stated. It's from a best practice guide, and it is a reasonable option where it is not practical/affordable to rewire the lighting circuit.
 
How is it reasonable? A sticker on the CU does nothing to improve safety.

I'd say that's nonsense, in those circumstances if it prevents someone who doesn't know any better from installing a metal fitting which could become live then it certainly has done something to improve safety ! Just because something isn't stated in black and white in the regs doesn't automatically make it a bad idea.
 

Reply to CPC/Earth feed to Light Switch Back Box in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock