Hey guys
Went to a customer today who wanted some electrical work looking at. Turned up and he showed me a granny annexe he had wired himself. (He has assured me he has 30years experience in the industry) he now wants it testing and certifying and a part p certificate issuing. I’m not comfortable with putting my name to the install and doing an electrical installation certificate. What would you do in this situation and what are his options.
 
I take photos of my 1st fix so possibly the guy has done the same..
If not floor boards will need to be lifted for inspection.
This may well satisfy building control for the installation methods.
Design is easy enough to verify along with testing too.
Can’t do an EICR on a brand new installation that has never been certified to start with
 
I take photos of my 1st fix so possibly the guy has done the same..
If not floor boards will need to be lifted for inspection.
This may well satisfy building control for the installation methods.
Design is easy enough to verify along with testing too.
Can’t do an EICR on a brand new installation that has never been certified to start with

Unfortunately that's how most BC offices approach the regularisation process.
 
How are the Napit/Stroma 3rd Party certifiers covered, if they’re only testing and notifying the work without seeing how it was installed? Do Napit/Stroma exempt their 3rd party notifier contractors from any prosecution etc?
 
How are the Napit/Stroma 3rd Party certifiers covered, if they’re only testing and notifying the work without seeing how it was installed? Do Napit/Stroma exempt their 3rd party notifier contractors from any prosecution etc?


Both schemes insist that the third party signer is present from before the job commences. They must produce the design, inspect all cable routes at first fix, inspect at second fix and perform all testing.

For the record Stroma, my chosen scheme, say they only offer this service as the government request this through the requirements of the building regulations, but they don't encourage use of the third party scheme at all.
 
How are the Napit/Stroma 3rd Party certifiers covered, if they’re only testing and notifying the work without seeing how it was installed? Do Napit/Stroma exempt their 3rd party notifier contractors from any prosecution etc?

But they should be seeing it at the install stage.
 
An EICR should not be used to certify new work, this is made clear in bs7671.

You could carry out the inspection and testing and and issue an EIC with the customers details and signature in the design and construction sections, you would only sign for inspection and testing.
But I wouldn't notify it for part P through a scheme, leave it for the customer to deal with building control directly.
 
To be honest if the guy was genuinely in the trade 30 years he should know it is a legal requirement to inform BC at least 48hrs prior to starting work. The fact he has not would already make a lie of what he is saying. As stated by @Dustydazzler third party requires being in at the beginning and design as well as first fix and dead tests as you go. Stroma are very strict about this and have their own form for 3rd party and effectively you have to sign you have complied with their requirements. So no retrospective sign off is possible via that route.
 
Can't see the problem if you are able to closely supervise the design, install with access to all aspects and test. You can then safely say its your installation....you wouldn't if it was a lash up. Similar to supervising a mate or apprentice.. presumably? There will be varying levels of competence and if its not there you'll be effectively doing the installation yourself due to the work involved in checking, testing and correcting and... charging accordingly :p
 
An EICR should not be used to certify new work, this is made clear in bs7671.

You could carry out the inspection and testing and and issue an EIC with the customers details and signature in the design and construction sections, you would only sign for inspection and testing.
But I wouldn't notify it for part P through a scheme, leave it for the customer to deal with building control directly.
No one’s suggesting that an EICR can be used to certify work Dave (at least I'm not)
But what you can't do is issue an EIC now, that bird has already flown.
All that you can do is, at the client’s request, undertake an electrical inspection and issue an EICR. What the client does with it is entirely up to him.
 
from the custmers thinking can some give me a get out of jail card.
Im sick and tired of this goverment
and the ones before eat of the land Prescott not informing the country about it insead of Chinese wispers.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Customer wiring own electrics
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
61
Unsolved
--

Advert

Thread statistics

Created
Sb8389,
Last reply from
Midwest,
Replies
61
Views
6,272

Advert

Back
Top