Hi all, I've just been asked to disconnect a 3 phase compressor. Not having done this before is it just a case of power off, disconnect then power back on or is there something special I'm missing out or need to consider?
Regards.
 
find where the 3ph compressor is fed from. isolate it. test dead at the copressor, check your tester on a known supply, and check dead again. disconnect compressor. I would perosnally lock the isloator off, if it has one. If not, and it is fed straight from the board, then i would personally disconnect the cables also from the breaker.

If you are still not sure, than ask someone to assist you Ie supervisor, or more experienced sparks
 
If it purely electrical then you just need to disconnect and make the circuit safe.

If responsible for the air side then you need to make sure that the system is not pressurised before you start undoing couplings and sorts. Though most will have non return vlaves fitted, not rote that they work. So turn off and normally there are ball valves on the accumalator which you open that will vent the air. Don't worry if you get a little water as well, as that will be normal.
 
Cheers Johnboy, that's exactly what I expected so no surprises there. Just thought that there might be something extra that I needed to take into consideration that I was over looking. As I'm recently qualified and starting out as self employed this will be the first invoice I've ever sent out. My question is a daft one but do you charge VAT on labour?
Regards.
 
your spot on johnny but I stupidly enough thought he was as he asked the VAT question. Then realsed as soon as I sent it that the chances are he wasn't

So to clear up if your VAT registered then you do have to charge VAT on labour
 
Just one to note chaps,

I have heard that the way they calculate to see if you should be paying VAT may be no longer down to yearly turnover.

The limit will be divided into 12 and if you exceed the monthly allowance three times in a row then you will need to be registered.

All word of mouth at the mo tho.
 
find where the 3ph compressor is fed from. isolate it. test dead at the copressor, check your tester on a known supply, and check dead again. disconnect compressor. I would perosnally lock the isloator off, if it has one. If not, and it is fed straight from the board, then i would personally disconnect the cables also from the breaker.

If you are still not sure, than ask someone to assist you Ie supervisor, or more experienced sparks

Tut tut, you know thats not the done way anymore ;)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Disconnecting a 3 phase compressor
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
lish70,
Last reply from
johnboy6083,
Replies
12
Views
2,525

Advert

Back
Top