I think you'll always get plonkers in trades and on forums. It's life.

But you can hold your head up high if you crack on and do the job right.

If it's 'the done thing' it doesn't mean it's right.
 
The regs do say you can't install a car charging point outside with exported PME.

From that we can infer we shouldn't be taking PME outside. Perhaps?
 
My knowledge and understanding is sound, ... I don’t have to justify a single thing to anyone here,
Lets examine the facts. You've made (bkanket) statements that other people who understand the issues didagree with (professionally). You've failed to provide any reasonable justification as to why your professional opinion is more valid than anyone else. You've also failed to provide any references to back up your position.
You then resort to insults, and an "I know thus stuff" attitude rather than answer reasonable questions.
I've made my mind up what sort of sparky you are - not one I'd employ ! Others can make their own minds up.
The regs do say you can't install a car charging point outside with exported PME.
From that we can infer we shouldn't be taking PME outside. Perhaps?
It's not that simple - and you can use an exported PME earth with the right considerations. In fact, the limitations are such that few will be able to use a TT earth and must use the PME earth.
It's interesting to observe that for a long time the rules has been "thou shalt not switch the protective earth, ever", yet now we have a subset where the earth must be switched :confused:
 
The regs do say you can't install a car charging point outside with exported PME.

From that we can infer we shouldn't be taking PME outside. Perhaps?
TBH I don't know enough about EV chargers to say exactly why PME isn't allowed. At a guess I would assume the same reason as caravans - a large metal object that is touched frequently by people standing on bare ground. If you lose the dno neutral the odds of someone getting a shock are high.

Compare that to a wooden summer house, wooden insulating floor, no extraneous parts. The risk here is no higher than in the main building, possibly less.

Assess on a case by case basis
 
  • Like
Reactions: Micktw68 and DPG
It is mainly for the risk of open circuits as I understand it, Regarding EV charging sockets. I was always told PME outside was risky mainly due to the possibility of the potential difference between the supply earth and the general mass of earth. Due to the volt drop if the run is long, from the transformer to the out building, but a risk assessment is always the best way to go,
 
“Suppose you TT an outbuilding, bonding the extraneous metal water pipe that originates (and so is bonded) in the main, TN-C-S supplied building. If we lose the DNO neutral, that pipe is going live along its length, both in the main building and the outbuilding, along with everything else bonded/earthed out there. Now we have the worst of both earthing arrangements, doubling the risk.”

That’s assuming that you are taking a metal pipe out there, and not poly, so in that case you would precautions to not let this happen.
The main reason why I am so strong for not taking PME outside, is when I did my 18th update, I was taking to an engineer who works for SSE, his job is to locate and fix, floating neutral faults on PME supply cables, he was very knowledgeable about this supply type. He could not state enough how dangerous it is under fault conditions, he even went on to say if his house had a PME supply, he would disconnect it and make his house TT.
I was also taught this when I was doing my 2330 lev3, my NVQ3 and my inspection and test.
I would put PME down as a C2 on an EICR if I saw that it was taken outside.

You cannot code an observation on an EICR based on your opinion, you can only code it according to bs7671. Currently there is nothing in bs7671 to support your suggestion of a C2 for a PME earth used for an outbuilding.

Yes PME has its downsides, but it is a very reliable earth connection for the vast majority of the time. You talk about it as if supplies to installations suffer neutral faults on a regular basis, they don't.
 
You could always add your own earth rod, so if there's a PEN failure you can earth the whole street :oops:
Wasn't there talk of that being made mandatory in the last update to the regs ?
 
You could always add your own earth rod, so if there's a PEN failure you can earth the whole street :oops:
Wasn't there talk of that being made mandatory in the last update to the regs ?

I think it got removed luckily.
 
  • Like
Reactions: Midwest
Not totally removed, I found this the other day in the OSG chapter 4.
 

Attachments

  • A101868A-6EC7-425C-B808-B5B93C7E72E9.jpeg
    A101868A-6EC7-425C-B808-B5B93C7E72E9.jpeg
    111.2 KB · Views: 23
  • Informative
Reactions: Pretty Mouth
You could always add your own earth rod, so if there's a PEN failure you can earth the whole street :oops:
Wasn't there talk of that being made mandatory in the last update to the regs ?

Yes you can, that's how it's done in a lot of other countries and is a good thing in my opinion.
It was going to be included in the 18th but I think it has been delayed for an ammendment.
[automerge]1574779340[/automerge]
The regs do say you can't install a car charging point outside with exported PME.

From that we can infer we shouldn't be taking PME outside. Perhaps?

The regs don't say this at all, they have certain requirements for car chargers connected to a PME supply.
 
  • Like
Reactions: DPG
Yes you can, that's how it's done in a lot of other countries and is a good thing in my opinion.
It was going to be included in the 18th but I think it has been delayed for an ammendment.

Thats alright, until you come to do a CU change on the top floor flat.
 
Thats alright, until you come to do a CU change on the top floor flat.

Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
 
Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
Not necessarily, some establishments are not so simple. I recall from some of the comments placed on the draft, asked this conundrum and allegedly why the committee put the reg change on hold for the time being.
 
  • Like
Reactions: DPG
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
 
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
It will be a similar requirement to that of EV installations where an additional electrode connected to the PME arrangement, during an open pen circuit the touch voltage from exposed parts to true earth must not rise above 70v (hand to foot for EV but may require to be 50v hand to hand contact between exposed parts)
This in reality is hard to achieve as per examples in section 722 annex and guidance note 5 and 7 examples.
[automerge]1574883321[/automerge]
Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
That’s a sweeping statement considering there are many set ups where flats have their own DNO supplies complete with metering and are situated on many floors, be it older type accommodation/schemes.
 
Last edited by a moderator:
  • Like
Reactions: Pretty Mouth
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
As I understand it, say the PEN breaks in the road, the current from let’s say house 1 (brown phase) They are using 50 amps, it a family of 4 at dinner time. That current is still going to try and flow back to the transformer but can’t, so it will find the shortest path, which will happen to be up the neutral of house 2 (black phase) House two may only be a little old lady and she only has a lamp and her Tv on so say she is using 5 amps. What is start to happen is she is going to get 400v turning up at her, appliances. And things starting to go bang, it will add a picture of this as well. So if there was an earth electrode at each house, it might help dump some of that stray current to earth, and trip some protective devices.
 
  • Like
Reactions: Pretty Mouth
It will be a similar requirement to that of EV installations where an additional electrode connected to the PME arrangement, during an open pen circuit the touch voltage from exposed parts to true earth must not rise above 70v (hand to foot for EV but may require to be 50v hand to hand contact between exposed parts)
This in reality is hard to achieve as per examples in section 722 annex and guidance note 5 and 7 examples.

Thanks Ian, I'll have to take a closer look at that at the weekend with a fresh mind, there's no way I'll get my head around it now!
 
  • Like
Reactions: Ian1981 and DPG
A5729AD4-5BA0-4DC8-B473-DE2388D9DDBE.jpegSome examples 7602A9F5-C629-4B1A-9B5F-E2C920477668.jpegsome examples
 

Attachments

  • C9447276-D6EF-4725-903B-CC701FD5ACBE.jpeg
    C9447276-D6EF-4725-903B-CC701FD5ACBE.jpeg
    98.9 KB · Views: 7
  • Like
Reactions: DPG
  • Like
Reactions: Ian1981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
DNOs forbid PME earth being exported???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
38

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Pretty Mouth,
Replies
38
Views
12,912

Advert