HI all. I am not an electrician and know only but a few things about it so I want to ask a question .
So Chargemaster is supposed to install a home charging unit on my property. Their technician came and said I needed additional electrical work (either an double pole isolation switch or run a 6mm cable from my board next to the main distribution and change a breaker from 16 to 32. I went for the 2nd option as it was cheaper.
The other thing he asked was to call my DNO to lower my earthing as my Ze was 0.44 on a TCNS system and they need it 0.35 and lower.
UK Power Networks does not offer appointments and they deal as if and when they are available on last minute notice so it can take forever.
When the electrician came to run the cable I asked him to measure the Ze and he found it at 0.24
1) Can the Ze change from day to day or time to time or did someone get it wrong (I think the Chargemaster one because he didnt very keen to work that day)
2) Could the whole Ze thing be bypassed if they install an earthing rod with the charging unit (I know Chargemaster does that but their technician did not even mention it)
Thank you all for the help in advance
So Chargemaster is supposed to install a home charging unit on my property. Their technician came and said I needed additional electrical work (either an double pole isolation switch or run a 6mm cable from my board next to the main distribution and change a breaker from 16 to 32. I went for the 2nd option as it was cheaper.
The other thing he asked was to call my DNO to lower my earthing as my Ze was 0.44 on a TCNS system and they need it 0.35 and lower.
UK Power Networks does not offer appointments and they deal as if and when they are available on last minute notice so it can take forever.
When the electrician came to run the cable I asked him to measure the Ze and he found it at 0.24
1) Can the Ze change from day to day or time to time or did someone get it wrong (I think the Chargemaster one because he didnt very keen to work that day)
2) Could the whole Ze thing be bypassed if they install an earthing rod with the charging unit (I know Chargemaster does that but their technician did not even mention it)