I assume it was written by someone who doesn’t speak English as a first language as there are numerous spelling mistakes and terrible grammar.
That in itself doesn’t make it a bad report.
On the face of it he’s managed to test an awful lot in 45 mins. Maybe he was there longer or had access to a previous report and has just copied that?
Some of the C2’s and C3’s are extremely harsh in my opinion.
[automerge]1593958473[/automerge]
I personally would’ve definitely coded no RCD on lighting as C3. This requirement only came in with the 18th in 2018. Strangely enough he has coded C3 for cables buried in wall less than 50mm, yet this regulation has been around since the start of 17th edition. Makes no sense to me. This one is almost certainly far too harsh unless there are lights/fans within the bathroom zones or something.
No RCD on socket outlets in 8th floor flat would be C3 for me probably. No chance of using equipment out of doors. However this would depend on whether sockets were positioned in places I would consider greater risk/there being electric under floor heating on the circuit etc.
IP rating of light fittings out of bathroom zones is not usually a reason to code at all in my opinion.
I have no idea what he’s waffling on about when talking about NIC.