A solar PV system keeps tripping the 30ma B curve RCD (at dawn).

The system is a TNC-S and the cabling to the inverter is surface mounted SWA.

Is there any reason to not swap the 30ma main switch out for a 100ma ?
 
He probably means a B type RCD.
So it’s only tripping when the DC cables polarise at the start of generation?

Seems so from customer reports. He's been resetting the RCD and the system is working fine after that. Of course dawn is around 5.15 at the moment so he's missing out on a lot of FIT.
 
Would you know if the Sunny Boy is:

a. transformerless?
b. is disconnected from the SWA cable until PV generation starts?

One thing to look at (from netblindpaul#8) is how tightly have the dc cables been clamped around their insulation to any metalwork.

If there is more than one Sunny Boy (I expect so) can you disconnect one in turn and leave the others on-line to see if the problems goes away?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Fitting a 100ma RCD on Solar PV to solve nuisance tripping.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
53

Advert

Thread statistics

Created
South Spark,
Last reply from
Nigel,
Replies
53
Views
12,332

Advert

Back
Top