If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
 
Where was the other lead of the DMM, still the MET? Did you measure the AC voltage? That would cause a symmetrical influence on the resistance readings. I agree though that some electrolytic potential does usually show up that at least makes a difference between the two indications, or even swamps the DMM source making one of them negative.
 
  • Agree
Reactions: static zap
Yes, it was basically the same test points. It was starting to rain so I didn't spend much more time checking AC volts, etc, but as the system is not finished yet there will be a more formal test when its all done.
 
No major question really. Screwed in a 2m long M16 stainless rod for earth today and got around 10 ohms which was better than I planned, but not desperately surprising as its clay soil and only a couple of meters above the river's mean level (i.e. water table).

Measured Zs extension lead to MET = 1.5 ohm, Zs same extension lead to rod = 11.5 ohm.

But what was odd was a DC resistance test (DMM, after low-ohm meter said > 100R) was showing around 170-200-ish ohms in both polarities. I expected I might see a DC bias, but did not expect that sort of non-linearity!
10 ohms. That must get you an automatic nomination for "rod of the year award". Well done
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
 
I expected about 4 times that to be honest!

There will be another 4 rods going in as well, but they are all more for lightning / EMC issues than power feed grounding. But it is still nice to know that if your TN-S supply earth goes open then you can still disconnect on the 300mA incomer RCD.
Absolutely. I have never heard of such a good result. Very encouraging. Yes a great plan B for TN-S. But with those soil conditions another 2 rods could quite possibly get you a plan B for a TNC-S Istallation as well. Wish we had conditions like that over here
 
  • Like
Reactions: pc1966
Wish we had conditions like that over here
Electrically it is way better than I expected. But there is a down-side to the wet clay below the local ground surface: when you get it on your shoes it behaves, in every way but smell, like you have stood in a dog turd!
 
Electrically it is way better than I expected. But there is a down-side to the wet clay below the local ground surface: when you get it on your shoes it behaves, in every way but smell, like you have stood in a dog turd!
Bearing out the old saying "nothing in life is free"
 
I think a reading below 200ohms is good and not unstable this is from the 16th ed
 
  • Disagree
Reactions: davesparks

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Happy earth rod day
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
pc1966,
Last reply from
jay sean,
Replies
8
Views
1,616

Advert