Hi Folks

Sorry, cable rating question! No doubt this has been asked before and I apologize profusely for not trawling the boards to find it but time is short.

Part of my brief is to install two 13 amp single sockets with single core on a radial circuit, (its less than 30m length and in PVC conduit) my notes say it should be 2.5mm 2 core and earth, but the brief says single core. Can you get single core 2.5mm? should i just use 2 core?

Also its protected by a 32A MCB but i thought 2.5mm had a rating of about 22A? And it could potentially draw 26A! whats with that?

I think I've been looking at this too long and just got myself confused, can somebody dig me out of this.

Many thanks

Lazy Student
 
in conduit, you use single cables. i.e. a brown, a blue and a gn/y. if 2.5mm cable on a 32A MCB, then make it a ring. sssimplesoops, just seen you stated a rfadial. use 4mm or 6mm singles then.
 
Thanks Telectrix.

That was my first thought but the lecturer poo pooed it for some reason, cost maybe. Either way I'm pretty much past caring so that's what i will do.

Fancy explaining why the regs let you put a 32 A MCB on a 22 A cable?

Thanks again

Lazy
 
You need to understand the concept of a ring final circuit. 2.5mm can carry up to 27amps depending on installation method. So, obviously you couldn't use a 32amp OCPD to protect it in a radial configuration. When wired as a ring, you have 2 x 2.5mm cables supplying the accessories. However, it's not quite so simple as if you had 2 x 2.5mm in parallel, as the amount of current each cable will be carrying will vary depending on the position of the load on the ring. This is why thought must be given to balancing the load on a ring, so as to avoid overloading one leg. :)
 
so give the lecturer this little gem. shoots him out the water. Iz>In>Ib.
 
about the same hope that there is for that 2.5mm cable getting hot while the 32A breaker just sits there, happily shoving 40A down it.
 
put it on a 16amp type b mccb.

bsen60898.

or if you want to be clever put it using 2.5mm tri-rated pvc singles.

a 32 amp breaker is too high for a radial using 2.5mm
 
Hi Gents

Kingeri, I think I was told that it was suitable for a radial, something to with sustained current, and he pointed me to the regs, sadly i don't have a copy of them now when i need them, but yeah it didn't seem right.

Telectrix, will do, but I'll wait till he has marked this,I think I will need him to be lenient.

Sintra, I think the mistake is more likely to lie with me than him.

Thanks for taking an interest lads

Lazy
 
ok ill explain why your getting confused with your notes.

depending on the installation method dictates which type of cable to use.

for example

cliped direct,conduit,trunking,ducting etc.

if your using clipped direct you normally use twin and earth (2c+earth)

in conduit,trunking etc you dont need the extra layer for mechanical protection so you just use singles.


now this is only applicable to this scenario and installation method
 
Cheers Shanky, if carrying capacity is 13.5 A and i've got two 13A sockets and i run a ring final should i use a 25 A MCB?
 
no mate. by 13amp socket its the max it can pull.


let me respond to your question with a question.

if your house has 2 ring circuits on 32amp mcb's. a 60amp cooker mcb and a 32amp shower circuit.

why has it only got a 100amp incoming fuse?

its all to do with diversity mate

(type b mcb's come in 6,10,16,32, etc)


remember the mcb is to protect the cable not the device.

i recomend you buy the onsite guide and have a read through it

www.amazon.co.uk/gp/aw/d/1849192871/ref=mp_s_a_1_1?qid=1370374964&sr=8-1&pi=SL75
 
As an Amazon Associate we earn from qualifying purchases.
Cause none of them are expected to pull their max. so i just need enough to protect the cables 16A MCB?
 
CCC of 2.5mm in conduit , ref. method B , is 24A so a 20A MCB would be appropriate.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help a poor student whose hand in is tomorrow!!!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
lazy student,
Last reply from
lazy student,
Replies
16
Views
1,746

Advert

Back
Top