Hi Folks

Sorry, cable rating question! No doubt this has been asked before and I apologize profusely for not trawling the boards to find it but time is short.

Part of my brief is to install two 13 amp single sockets with single core on a radial circuit, (its less than 30m length and in PVC conduit) my notes say it should be 2.5mm 2 core and earth, but the brief says single core. Can you get single core 2.5mm? should i just use 2 core?

Also its protected by a 32A MCB but i thought 2.5mm had a rating of about 22A? And it could potentially draw 26A! whats with that?

I think I've been looking at this too long and just got myself confused, can somebody dig me out of this.

Many thanks

Lazy Student
 
in conduit, you use single cables. i.e. a brown, a blue and a gn/y. if 2.5mm cable on a 32A MCB, then make it a ring. sssimplesoops, just seen you stated a rfadial. use 4mm or 6mm singles then.
 
Thanks Telectrix.

That was my first thought but the lecturer poo pooed it for some reason, cost maybe. Either way I'm pretty much past caring so that's what i will do.

Fancy explaining why the regs let you put a 32 A MCB on a 22 A cable?

Thanks again

Lazy
 
You need to understand the concept of a ring final circuit. 2.5mm can carry up to 27amps depending on installation method. So, obviously you couldn't use a 32amp OCPD to protect it in a radial configuration. When wired as a ring, you have 2 x 2.5mm cables supplying the accessories. However, it's not quite so simple as if you had 2 x 2.5mm in parallel, as the amount of current each cable will be carrying will vary depending on the position of the load on the ring. This is why thought must be given to balancing the load on a ring, so as to avoid overloading one leg. :)
 
so give the lecturer this little gem. shoots him out the water. Iz>In>Ib.
 
With lecturers like that what hope is there for the future of this game.
 
about the same hope that there is for that 2.5mm cable getting hot while the 32A breaker just sits there, happily shoving 40A down it.
 
Hi Gents

Kingeri, I think I was told that it was suitable for a radial, something to with sustained current, and he pointed me to the regs, sadly i don't have a copy of them now when i need them, but yeah it didn't seem right.

Telectrix, will do, but I'll wait till he has marked this,I think I will need him to be lenient.

Sintra, I think the mistake is more likely to lie with me than him.

Thanks for taking an interest lads

Lazy
 
ok ill explain why your getting confused with your notes.

depending on the installation method dictates which type of cable to use.

for example

cliped direct,conduit,trunking,ducting etc.

if your using clipped direct you normally use twin and earth (2c+earth)

in conduit,trunking etc you dont need the extra layer for mechanical protection so you just use singles.


now this is only applicable to this scenario and installation method
 
no mate. by 13amp socket its the max it can pull.


let me respond to your question with a question.

if your house has 2 ring circuits on 32amp mcb's. a 60amp cooker mcb and a 32amp shower circuit.

why has it only got a 100amp incoming fuse?

its all to do with diversity mate

(type b mcb's come in 6,10,16,32, etc)


remember the mcb is to protect the cable not the device.

i recomend you buy the onsite guide and have a read through it

www.amazon.co.uk/gp/aw/d/1849192871/ref=mp_s_a_1_1?qid=1370374964&sr=8-1&pi=SL75
 
CCC of 2.5mm in conduit , ref. method B , is 24A so a 20A MCB would be appropriate.
 
As a reference for both you and your tutor I would refer you to Appendix 15 of BS7671:2008 Ring and Radial Circuit Arrangements : Regulation 433.1 on pp425.

Regulation 433.1 in the title of the Appendix directs the reader in pp81 and specifically 433.1.103, I strongly suggest you read it before proceeding and ensure you understand it.
 
Ok having got a copy of the regs (don't ask how i did that at 11pm), I think the problem arose because I had forgot that the circuit is "unlikely to exceed for long periods of time the current carrying capacity of the cables" (433.1.5)

Cheers for all the help gents

Lazy
 

Reply to Help a poor student whose hand in is tomorrow!!! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi All I’m in a bit of a quandary at work and need a couple of things clearing up if poss. I’m the maintenance...
Replies
11
Views
2K
Hello, So I'm an idiot homeowner who has enough knowledge to be dangerous.. I tried to make my own shortcut by tinkering and I seem to just be...
Replies
1
Views
1K
Hi Folks, I am in the process of building a log cabin in the garden and I am in need of some advice when it comes to the electricity supply. I...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock