I tried to make this post as detailed and clear as possible, to get the best advice. It is therefore long. 
We bought a house that was built in the 90s. There is an outbuilding with a subpanel in it about 300 feet away. This subpanel is supplied by a 240V / 30A breaker in the main panel. Ordinary residential single phase power. 3 wires, two line and a neutral.
The outbuilding roof is the only suitable location for a solar array, and we want to put about 5KW on it, fed back to the home over the existing line.
Even at max theoretical production (which solar arrays never hit, and our install certainly wouldn't due to not-quite optimal orientation and panel angle), 5000W at 240V is just ~21 A, so this existing circuit appears adequate to carry the array's output back to the home.
The area where I think there might be a problem is that they used 10g wire for the run (buried). This seems rather undersized for the distance.
The drop calculator at Southwire's web site estimates a 10.49% voltage drop for a 20A load at 120V, a 5.25% drop for a 10A load at 120V, and 7.87% for a 30A load at 240V. That seems to be not OK.
I went ahead and measured actual voltage drops from the main panel to the subpanel, with no load and under two different loading conditions. I have an Iotawatt monitor installed in the main panel, so I get accurate realtime readings of the load to the house as a whole and various circuits, including both legs of the 240/30A line to the outbuilding.
The results are a little puzzling and I'd like some help understanding them, and deciding if the wire buried in the ground actually needs to be upsized. (The existing setup has worked Just Fine for running lights and tools in that building for the 3 years we've lived here and presumably for the decades the previous owners did.)
For loading the outbuilding, I had three scenarios:
It was a little difficult to get all the readings with the same total load on the home, since the HVAC and other loads occasionally came on and off. But for each load condition in the outbuilding, I got main and subpanel readings with similar total household loads:
Measurements were made with a Klein CL390 meter directly at the main panel circuit breaker, and the subpanel input.
Voltage drops with ~2000 watt total load on home, and 70 + 3 watt load to outbuilding:
242.0 to 241.7 (-0.1%)
R 120.3 to 119.8 (-0.4%)
B 121.8 to 121.8 (no drop)
Voltage drops with ~4500 watt total load on home, and 965 + 1265 watt load to outbuilding
240.1 to 233.1 (-2.9%)
R 120.1 to 118.1 (-1.6%)
B 120.3 to 115.1 (-4.3%)
Voltage drops with ~4000 watt total load on home, and 1930 + 3 watt load to outbuilding
239.4 to 234.4 (-2.1%)
R 117.8 to 106.7 (-9.4%)
B 121.8 to 128.2 (+5.3%)
No surprise, no voltage drop with no load. I can wrap my mind around that.
Small surprise, with a balanced load of about 1000W per leg, there was somewhat less voltage drop than predicted by the calculator: 5.25% predicted but 1.6% and 4.3% measured. I guess that's not too far off predicted.
Weird surprise, with the unbalanced load of about 2000W on one leg and nothing on the other, a 9.4% drop on one and a 5.3% INCREASE on the other. I don't understand that
Can someone explain the measurements with the unbalanced load?
Will this arrangement be OK to leave alone? It has apparently worked fine without spontaneously combusting for 30 years.
Any thoughts about using the existing line to feed (at most) 5000W at 240v back to the main panel from a solar inverter? Even under load the total voltage drop was under 3% for the overall circuit.
There are two phases of permitting required for a DIY solar install. One from the county (which is primarily concerned with structural issues for the roof loads and zoning) and one from the power co for the grid tie. Eventually I'll pay for professionals to assess those things. But as I'm in the planning stages now, I'm trying to understand all of the issues and get an idea of what to expect.
Thank you.

We bought a house that was built in the 90s. There is an outbuilding with a subpanel in it about 300 feet away. This subpanel is supplied by a 240V / 30A breaker in the main panel. Ordinary residential single phase power. 3 wires, two line and a neutral.
The outbuilding roof is the only suitable location for a solar array, and we want to put about 5KW on it, fed back to the home over the existing line.
Even at max theoretical production (which solar arrays never hit, and our install certainly wouldn't due to not-quite optimal orientation and panel angle), 5000W at 240V is just ~21 A, so this existing circuit appears adequate to carry the array's output back to the home.
The area where I think there might be a problem is that they used 10g wire for the run (buried). This seems rather undersized for the distance.
The drop calculator at Southwire's web site estimates a 10.49% voltage drop for a 20A load at 120V, a 5.25% drop for a 10A load at 120V, and 7.87% for a 30A load at 240V. That seems to be not OK.
I went ahead and measured actual voltage drops from the main panel to the subpanel, with no load and under two different loading conditions. I have an Iotawatt monitor installed in the main panel, so I get accurate realtime readings of the load to the house as a whole and various circuits, including both legs of the 240/30A line to the outbuilding.
The results are a little puzzling and I'd like some help understanding them, and deciding if the wire buried in the ground actually needs to be upsized. (The existing setup has worked Just Fine for running lights and tools in that building for the 3 years we've lived here and presumably for the decades the previous owners did.)
For loading the outbuilding, I had three scenarios:
- nothing on except a network switch on one leg (70W + 3W)
- lighting and space heater on different legs (965W + 1265W)
- lighting and space heater on one leg (1930W + 3W)
It was a little difficult to get all the readings with the same total load on the home, since the HVAC and other loads occasionally came on and off. But for each load condition in the outbuilding, I got main and subpanel readings with similar total household loads:
Measurements were made with a Klein CL390 meter directly at the main panel circuit breaker, and the subpanel input.
Voltage drops with ~2000 watt total load on home, and 70 + 3 watt load to outbuilding:
242.0 to 241.7 (-0.1%)
R 120.3 to 119.8 (-0.4%)
B 121.8 to 121.8 (no drop)
Voltage drops with ~4500 watt total load on home, and 965 + 1265 watt load to outbuilding
240.1 to 233.1 (-2.9%)
R 120.1 to 118.1 (-1.6%)
B 120.3 to 115.1 (-4.3%)
Voltage drops with ~4000 watt total load on home, and 1930 + 3 watt load to outbuilding
239.4 to 234.4 (-2.1%)
R 117.8 to 106.7 (-9.4%)
B 121.8 to 128.2 (+5.3%)
No surprise, no voltage drop with no load. I can wrap my mind around that.
Small surprise, with a balanced load of about 1000W per leg, there was somewhat less voltage drop than predicted by the calculator: 5.25% predicted but 1.6% and 4.3% measured. I guess that's not too far off predicted.
Weird surprise, with the unbalanced load of about 2000W on one leg and nothing on the other, a 9.4% drop on one and a 5.3% INCREASE on the other. I don't understand that
Can someone explain the measurements with the unbalanced load?
Will this arrangement be OK to leave alone? It has apparently worked fine without spontaneously combusting for 30 years.
Any thoughts about using the existing line to feed (at most) 5000W at 240v back to the main panel from a solar inverter? Even under load the total voltage drop was under 3% for the overall circuit.
There are two phases of permitting required for a DIY solar install. One from the county (which is primarily concerned with structural issues for the roof loads and zoning) and one from the power co for the grid tie. Eventually I'll pay for professionals to assess those things. But as I'm in the planning stages now, I'm trying to understand all of the issues and get an idea of what to expect.
Thank you.