I have hooked up a 30 amp interlock switch to my main panel run off my generator. However, only my light switches work none of my plug-ins have any power. Any input would be helpful. Thanks.
 
My generator has a floating neutral. My light switches have neutral wires, but my plug-ins don't. Is that the problem?
 
My generator is a 30 amp 120 V
 
Honestly in this case I think that getting a qualified electrician in to survey what has been done so far and the best way to fix the problems is the best way forward.

There is a lot more to running a generator and using it to power a house than you might think, even if what you rig up "works" then it may still be dangerous.

Have a professional look at it PLEASE.
 
I have hooked up a 30 amp interlock switch to my main panel run off my generator. However, only my light switches work none of my plug-ins have any power. Any input would be helpful. Thanks.
It sounds like you are just getting 120vac instead of 240vac. Check your cord, and plug connections.
 
  • Like
Reactions: Megawatt
It's the same voltage in Canada as in the USA.
I know. But Megawatt said
“ It sounds like you are just getting 120vac instead of 240vac.”
Surely a Canadian (or. USA) genny would be expected to produce 120v. ??
Confirmed by the OP
My generator is a 30 amp 120 V
 
I know. But Megawatt said
“ It sounds like you are just getting 120vac instead of 240vac.”
Surely a Canadian (or. USA) genny would be expected to produce 120v. ??
Confirmed by the OP
Most installations are two-phase (split) 120V - 0V - 120V so it you do the simple and obvious you only get half the panel powered up. To run a typical USA house fully you need a generator has 120-0-120 out and a suitable transfer switch for both L and some means to deal with N.

They typically have PME supply with local Earth rods linked to the incoming point Earth/ground, and the N-E link inside the first (main) panel. That is unlike UK where linking N & E is only permitted on the DNO side before your meter, etc.

Presumably then you can switch the main panel incoming L1-N-L2 to the generator's output, with the rods still linked at the panel to earth-reference N while on generator. No idea if that meets NEC code!
 
Last edited:
  • Like
Reactions: Megawatt
My generator is a 30 amp 120 V
Well there's your problem. A 120 V generator outputs a hot and a neutral and a ground. Your electrical service and panel expect a 120/240 V output which is why the inlet breaker is a 2-pole 30 A variety. Your panel gets 2 120 volt lines from the utility, electrically 180 degrees apart to provide 1/2 of the breaker slots in your panel with 120 volts from line 1, and the other 1/2 of the slots with 120 volts from line 2. Your generator outputs 120 volts onto one leg in your panel only, the other 1/2 of the circuits are getting nothing. To power your home from a generator with an interlock you need a 120/250 volt generator unless you can live with only 1/2 the circuits in your panel.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Canada
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Canada
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Interlock switch, not powering all of my breakers
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Jason W,
Last reply from
RetiredNY,
Replies
10
Views
1,407

Advert