I had an inspection yesterday, where the lighting and sockets are in one circuit for each floor.
There are 3A fused spurs for the lights. I also need to replace the consumer unit with 18th edition one.
How would you code that? Any advice on the consumer unit would be appreciated.
ThanksHnet.com-image (1).jpg
 
Last edited by a moderator:
I wouldn't Code it at all. What does the EICR state, is it possible to show it with personal details removed.
 
Lights that are off a 3A FCU are perfectly safe.

You might code it C3 due to the lights failing if the sockets are tripped out (division of circuits 314.1).

That is an old looking CU but @westward10 is the best person to ask!
 
Lights that are off a 3A FCU are perfectly safe.

You might code it C3 due to the lights failing if the sockets are tripped out (division of circuits 314.1).

That is an old looking CU but @westward10 is the best person to ask!
Good question I initially thought Square D QOE but they are missing the indicator window and the rating is painted on the toggle, so not Square D.
Not a common brand that immediately hits me but could be Mitsubishi. The ON/OFFS look hand painted.
OP any info on the front off the open flap.
 
Last edited:
The other thing I'm wondering is what the "restricted" supply is, off-peak meter?
 
The other thing I'm wondering is what the "restricted" supply is, off-peak meter?
I would assume it is dual tariff but didn't notice the restricted wording.
 
Looks very much like crabtree c50 CU
 
Not a C50.
 
  • Like
Reactions: 7029 dave
Good question I initially thought Square D QOE but they are missing the indicator window and the rating is painted on the toggle, so not Square D.
Not a common brand that immediately hits me but could be Mitsubishi. The ON/OFFS look hand painted.
OP any info on the front off the open flap.
 
I thought it was the same as what’s dotted around that big test job I’m doing…. But they’re Dorman Smith…

IMG_3861.jpeg
 
Those are type 4, if they are flat around the toggle without the ridges then type 3🙃
Another thing, if they have some sort of addition to the terminal like a flat spring affair that is to increase their breaking capacity.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
ZV Electrics

Thread Information

Title
Lights and sockets on one circuit?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
zvspark,
Last reply from
westward10,
Replies
11
Views
2,063

Advert