The 3 phase service cut out for my block of 3 flats was recently moved.
The service head used to be tns. The new service head is tncs. This has not been marked up as pme.
My flat has a new 16mm earthing conductor(connection between old MET and new MET) , however the other 2 flats only have their existing 6mm feeds as part of 16mm twin and earth supplies.
Is the 6mm ok(assuming correct by adiabatic and I would be confident of this) or will pme rules apply and require 10mm.
I ask as although I know it was formerly tns, will someone else see tncs and immediately think pme and 10mm.
Please excuse my inexperience, I require no comment on it.