The over current protective device that is protecting each 16mm T&E.
63amp each I was planning to use
Discuss Multiple consumer units in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The over current protective device that is protecting each 16mm T&E.
63amp each I was planning to use
63a 30ma rcd
The thing is Eddie if you use an mcb for the distribution circuits then you have next to no chance of discrimination with the final circuits.
edit: An RCD doesn't provide over current protection.
if I ran swa out of a fused isolator switch for each submain would that provide me with the protection that I need dependant on demand etc
if I ran swa out of a fused isolator switch for each submain would that provide me with the protection that I need dependant on demand etc
Of course
Hope you get it sorted Eddie, I'm trying to keep up with this post and learn a bit more
Humans hay, keep learning and changing or fade away
Could you advise what would be best to do please
What size OCPD are you planning on using for the 4 x distribution circuits?
63a 30ma rcd
Yer I am going to cheers guys the issue regarding distribution has been the bit I have been stuck I want to get it right hence seeking advice on here I will get someone with more experience to come in and have a look but looks like I'm going to run it in swa i will properly calculate the csa's and get back to this forum afterwards, I appreciate this should have been done beforehand