Hi Pete999, here is a partial screenshot of a page of the doc.
file:///C:/Users/Pete/Downloads/BS_7671_2008_AMD3-2015_Model_Forms(3).pdfOther values I can see:
Nominal frequency: 50Hz
External earth fault loop impedence Ze (2/3): 0.57
Prospective fault current (2/3): 0.5
the report also states that he used for testing equipment, a Kewtech KT64 (might be 84, hard to read)
Page5of6 schedule of test resultsNot sure how to download files. However, here is a link to almost exactly the same form, I say almost because the layout of Scheduled Inspections has changed but not the content I don't think. This is the form. If you can show me where to see where those values should have been written then thanks.
http://www.electricaltestcertificat...estic-Electrical-Installation-Certificate.pdf
2nd line down LtoL IR over 200 Mohms that would indicate you have a 3 phase supply
to be fair, i'd put that down as a typo.2nd line down LtoL IR over 200 Mohms that would indicate you have a 3 phase supply
Not sure why he's put N/A for continuity of protective conductors?
I've never got rcd test results that low hahaSome circuits are run surface and should be rectified in future ?
Whats the world record for speed of reaction of a 30 m/amp Rcd ?
200 M/ohm across the board seems like a very common reading for insulation resistance of well used installations these days
The consumer unit is a 11 way,the test schedule lists 5 ways,the 2 Rcds seem to have 3 circuits each ,decisions,decisions,try as I will,I just can't make sense of what has been produced
Tails in photo don't indicate that. Personally I don't like exposed live bus bars either.3 phase supply
I've never got rcd test results that low haha
0.02 and 0.03 of a second
Edit
Or is it 0.2 and 0.3 of a second I can't make it out?
Just pointing out that either it was a typo (very likely) or the report is a fudgeTails in photo don't indicate that. Personally I don't like exposed live bus bars either.
Just pointing out that either it was a typo (very likely) or the report is a work of fiction
Thank you Murdoch, kind of you.Corrected that for you...
Vol, do you have a snap shot of the 'Circuit Details' and the 'Test Instrument Used'?
PS good that the dangerous fault has now been rectified. Its a shame your electrician didn't do all the form filling in and testing in the first place.
Hi Midwest, please refer to my post #135. "I've tried to show willing in response to the help I did get by showing as much info from today's resolution as I could. I'm done now." What part of "I'm done now" don't you understand?
The bit about you still being involved and contributing to the conversation?What part of "I'm done now" don't you understand?
I had this scenario after doing a full inspection and testing of a property last month. The test results were good and I installed a new split amendment 3 CCU. I then did some tests after the install and noticed I had L-N reversal at all sockets. I then rechecked my wiring/polarity at the board; all good. I eventually established that one of the main RCD'S was faulty. Considering it was brand new, I was surprised by this. The board was an MK Sentry,brand new. Theses boards are being sold at a much cheaper price than their main competitors but I won't be buying them anymore.Hi there, I'm a newbie to the forum. I'm an ordinary senior citizen householder but while not an electrician, I do take notice and read up on all the stuff the electricians are doing in my house. I have just had a modern, metal consumer unit installed after the removal of the old traditional fuse box. The installation went pretty well with very few curses!Given the old wiring in the house, everyone was pleasantly surprised when both RCDs stayed good and the supply uninterrupted.
As a final check before leaving, the electrician inserted a socket tester. In every location tried, the socket tester showed L&N Reverse. I bought s socket tester and confirm the same readings: L&N Reverse. I haven't checked every single socket but that is the pattern.
One problem is that I have no way of telling if the old fuse box situation would have given the same L&N Reverse readings, ie did the electrician change anything or just carry on an existing (hidden) error?
Firstly, is this in any way a dangerous situation given the RCDs are quite happy? If dangerous, what should be done immediately?
Secondly, how could this reversal have occurred? The electrician simply reinserted the live and neutral cables appropriately as they were removed. The meter tails were changed cos the existing were only 16mm. Could the tails have been reversed somehow?
Anything else you guys can suggest?
Thanks for reading the newbie panic post! I would appreciate any input, thanks..
try the BG boards. similar price to MK, but better quality and better looking. ( a bit like me, i supposeI had this scenario after doing a full inspection and testing of a property last month. The test results were good and I installed a new split amendment 3 CCU. I then did some tests after the install and noticed I had L-N reversal at all sockets. I then rechecked my wiring/polarity at the board; all good. I eventually established that one of the main RCD'S was faulty. Considering it was brand new, I was surprised by this. The board was an MK Sentry,brand new. Theses boards are being sold at a much cheaper price than their main competitors but I won't be buying them anymore.
What was the fault on the RCD?I had this scenario after doing a full inspection and testing of a property last month. The test results were good and I installed a new split amendment 3 CCU. I then did some tests after the install and noticed I had L-N reversal at all sockets. I then rechecked my wiring/polarity at the board; all good. I eventually established that one of the main RCD'S was faulty. Considering it was brand new, I was surprised by this. The board was an MK Sentry,brand new. Theses boards are being sold at a much cheaper price than their main competitors but I won't be buying them anymore.