N

Nibbosonline

Hi
I'm looking to buy a new double oven and induction hob to replace my very old ones. The current units are both wired to an double pole cooker switch nearby and then on via 6mm cable, under the wooden floor to the consumer unit about 15 feet away and a 30 amp fuse.

Having started looking at induction hobs I realise they can be quite power hungry and there are some "plug and play" versions that have a 13 amp plug and manage the power down. The shop told me I would have to have one of these but, although I'm not an electrician, this didn't ring true to me. I'd welcome some advice.

I thought that Electrical Diversity would allow me to replace the existing equipment on the existing circuit totaling about 15KW. Have I got this wrong?

best regards and thanks in advance.
Dave
 
Depends what you understand by diversity!

15kW on a 30A circuit would allow for less than 50% of the equipment to be used safely, fuse would(could) overload if trying to use too much at once.
General guidance for 15kW (ie 10A + 30% of FL etc) would be less than 30A, (approx 3rd of total load being used at any one time) therefore should be ok.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
New cooker wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Nibbosonline,
Last reply from
DefyG,
Replies
1
Views
1,188

Advert