I'm looking at the options for customer who has no CPC on lights as is quite common. I know the ESC "good practice guide" - and that all makes good sense.

However most light switches with exposed screws into metal back boxes (where metal box is unearthed because no CPC), would therefore be class 1. - I am looking here at a standard light switch directly outside the airing cupboard door (metal tank therein, touchy both maybe.. ).

Q) Might the ones with small plastic plugs (eg LAP 2-Gang 2-Way 10AX Light Switch White | Screwfix.com) be classified as Class 2 for the point of this exercise and be a suitable swap? They are not advertised as class 2, probably uncertified as that, but a safer bet than ones with exposed screw heads? (at least till someone looses the weeny button thingy) .

A related question. I guess BC lampholders are intrinsically class 1, but as they are right up there in the ceiling, what's the likelihood of Mrs Jones touching both the metal surround of her light holder (just as it fails L-E), and her radiator? If I assume normal length arms, I think we are safe here.. Where does one draw the line?
 
You must make sure the circuit is class 2 so light fittings and switches are plastic.

On the switch front then you can use either nylon pins to insulate between the metal back box and switch plate or using a switch that has plastic caps to cover the fixing pins

Then a label should be fitted to the consumer unit stating no metal fittings should be fitted and it should be noted on the electrical circtificate that this has been done and class 2 fittings fitted
 
On the switch front then you can use either nylon pins to insulate between the metal back box and switch plate or using a switch that has plastic caps to cover the fixing pins

Hmmm.. Nylon pins? Do you mean fit nylon screws the same thread? Maplin maybe..?

The plates with the little plastic pips are more for the visuals than specifically for Class 2, so do I take it that using these is common where we have this issue?
 
Hmmm.. Nylon pins? Do you mean fit nylon screws the same thread? Maplin maybe..?

The plates with the little plastic pips are more for the visuals than specifically for Class 2, so do I take it that using these is common where we have this issue?
just put the plastic caps over the screw heads...
job done...
 
I'll get some of those in then..

I shall also chose to ignore all those switches with high IR (L+N..screw head), unless within reach of extaneous parts. This will probably be most of them I think, as long as they are away from radiators and pipes.

Would you change BC fittings for ES?
 
I'll get some of those in then..

I shall also chose to ignore all those switches with high IR (L+N..screw head), unless within reach of extaneous parts. This will probably be most of them I think, as long as they are away from radiators and pipes.

Would you change BC fittings for ES?
no Justin...IR can break down...
get em covered ...like the others...
owt that could provide a potential here mate...
 
I'll get some of those in then..

I shall also chose to ignore all those switches with high IR (L+N..screw head), unless within reach of extaneous parts. This will probably be most of them I think, as long as they are away from radiators and pipes.

Would you change BC fittings for ES?
whats the existing fittings....if any are metal and no CPC ...get em dropped...
 
Well I should do so if that's the advice from the coal face.

The EIC best practice guide does say we can leave'em if > 1M Ohm..

BC fittings for ES: I am assuming BC has exposed metal surround which could become live if the L cable fell off internally and touched it. ES must normally be class 2 intrinsically, and I guess BC is class 1.
 
Hmmm.. Nylon pins? Do you mean fit nylon screws the same thread? Maplin maybe..?

The plates with the little plastic pips are more for the visuals than specifically for Class 2, so do I take it that using these is common where we have this issue?

Try these they insulate from the metal back box so no metal is showing and this means it is then class 2
http://uk.rs-online.com/mobile/p/machine-screws/0291414/

The switches with plastic caps comply with regs because it means that you Carnt touch the metal pins
 
a lot of the back boxes may have nylon lugs if they've not been changed from the original. pendant BC lamp holders are classII.
 
How can not earthing a metal back box be acceptable? Imo the best option is to remove the metal back box and replace it with a plastic surface box

if the above suggestions are followed, then it's perfectly acceptable. maybe not ideal but if the client won't pay for earthing to be added, nowt else you can do. and very few clients would accept ugly surface boxes. i know i wouldn't.
 
So whats going to happen when screwing the switch plate back and the cable nicks the counter sunk screw and the metal box is not earthed. I do a lot of domestic testing and have done for many years. I have always classed this type of installation as unacceptable.
 
it is unacceptable to install without earthing nowadays, but you can't condemn an older installation that was installed in accordance with the regs. at the time.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

1Justin

Arms
-
Joined
Location
Surrey
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Circitas Ltd

Thread Information

Title
no CPC on lights, - switches for class 2?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
1Justin,
Last reply from
telectrix,
Replies
37
Views
12,174

Advert

Back
Top