Hi all , im new here but have always looked for answers over the months

description of my question
there is an external 100 amp 3 phase metered head that this new 10 bed house is to be fed from , the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth

now is my only option to treat this a a tt supply or a really stupid question is can i simply make it a pre from the neutral at my distribution board (as it would be the same as whats at the source ) obviously not but it would definatly be easy

now over the last 20 or so years i have not ever done a tt supply (not since collage anyway) do i need to drop earth rod then cover the new 3phase dis board with a 30 ma main switch or can i install 100ma main switch and then protect all circuits with planned rcbos as original plan

also one more thing , was i right in thinking that i was never allowed to take the earth from the pme head regardless to if the builder had remembered the earth ?

so many questions

and thanks
 
yes you right Murdoch , and KEV 1N you have to have a separate earth if you have to install main bonding within an installation
Ive seen loads of buildings done this way, example: University colleges, the main building will have the incoming supply to a large section board and its own earth bar for water, gas etc, then SWA cables feed the other accommodation buildings to their own section boards and earth bars ...no separate earth conductor.
 
You did say it is a PME supply? So why not use the terminal at the cut-out??? Sorry if I missed something. What or where is the 35mm² SWA coming from and to and how far?
 
As far as I know, since the installation earth is taken at source (before your swa) then you can't take it again further down the supply.
 
Kev 1 N , i covered this issue of using the steel wired as main earth resonantly within a 5 yearly of an office block as after calling the NICEIC help desk and then covering it on my last yearly visit was told the earth cable required if your earthing main water or steel work gas etc etc (he even handed me a few A4 sheets on it ) (the know it all lol)
Vortigern , 4 core 35mm swa from main supply head , its about 35meter stretch (under block paving and slabs not an easy route ) and when you say cut off do you mean at the main switch at the planned new dis board within the house ?
 
Just out of interest (maybe should start a new thread but after being on here for months still can't work out how), is the steel in SWA manufactured to be the correct ratio csa to the cores, bearing in mind it has a higher resistivity etc? Don't know why I have just thought about this but I have blindly used the armour as a cpc before without checking this!
 
Ok now I see you can't retrospectively (easily) come from the pme terminal at the main service head (cut-out) But I don't get how you can join SWA into the main cut-out. What about the gland etc. Just ignore me if you think that is dumb. You can even give me a dumb rating I'm a bit short on them.o_O
 
I think this comes from Reg 543.4.1
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
 
Well if it's in the regs, then it's in black and white....just seems maddnes having a good earth at the DNO cutout, then at the DB end ditching it and then put in earth rod. Again , the University has several of its own substations with massive section boards that feed other large buildings (so technically the substation is the DNO supply) so then there'll be say 3 or 4 300mm2 SWA cables go out to feed other buildings, no separate cpc, then when they enter the building, an earth conductor is took off the armour to an earth bar and then from that you'll have a main protective conductor to the buildings section board, and protective earthing conductors to other services.
The armour of those cables may be adequate to support bonding.
 
thanks for comments guys , i need all phases as massive house with a lift and various kitchens with big appliances etc , but i guess the main switch being 300ma rcd then me using 30ma rcbo units is the way , there is a 6 inch duct howeve its not a straight route and they didnt pull in a draw wire just the cable (bless them )
 
The armour of those cables may be adequate to support bonding.
Ah so smaller SWA cables may not be suitable for that. Funnily the cables I've seen used in this way were much bigger that 35mm2, 50mm upwards if I remember correctly.
 
thanks for comments guys , i need all phases as massive house with a lift and various kitchens with big appliances etc , but i guess the main switch being 300ma rcd then me using 30ma rcbo units is the way , there is a 6 inch duct howeve its not a straight route and they didnt pull in a draw wire just the cable (bless them )
Well I suggest you get a pet rat and train it to run through drain pipes with string tied to it, put it through your duct, then tie a rope to the string, then use rope to pull in earth cable.....job done;)
 

Reply to PME head , builder forgot earth cable , 100amp 3phase supply , 10 bedroom house , 10 bedroom house in the The Welcome Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top