Okay, I know this question pops up a lot but I want to be really specific, and ask in the trainee bit for your thoughts.
I've done my first inspect & test assignment, and one of the questions is "show using the help of a diagram the earth fault loop path for an earth fault in the lighting circuit of the workshop".
So I drew this rather crude drawing (attached)
As you can see, the path goes through the relevant DBs, using the armouring of the distribution circuit as the earth to the workshop, and then eventually through the PEN conductor back to the transformer.
On Monday the tutor asked me how I was doing, and me being a clever sod said I was about done. He said he'd bet any money I'd done this question wrong and when I asked him he explained it was because the workshop needed a rod.
I argued it didn't because the armour of the SWA was sufficient to act as the CPC of the circuit (16mm SWA, 33A total load, 75m run, armour is much more than sufficient). There are no extraneous items in the workshop that need bonding, so my view (heavily based on the opinions of this forum) is that it is perfectly safe to take the supply earth out to the workshop. For info, the workshop is wooden construction on a concrete base.
Now I think I can see where my tutor is coming from about safety. If there was a lost neutral all earthed parts would become live. This might not be a big issue in the main building, but maybe there is a chance of someone using a metal tool outside the workshop and is stood directly on the ground. Then we'd have an issue.
So, I was thinking that a rod is not strictly needed by the letter of the law, but the more I ponder it the more I think it might be a sensible idea to put a rod in.
Just wanting peoples thoughts?
I've done my first inspect & test assignment, and one of the questions is "show using the help of a diagram the earth fault loop path for an earth fault in the lighting circuit of the workshop".
So I drew this rather crude drawing (attached)
As you can see, the path goes through the relevant DBs, using the armouring of the distribution circuit as the earth to the workshop, and then eventually through the PEN conductor back to the transformer.
On Monday the tutor asked me how I was doing, and me being a clever sod said I was about done. He said he'd bet any money I'd done this question wrong and when I asked him he explained it was because the workshop needed a rod.
I argued it didn't because the armour of the SWA was sufficient to act as the CPC of the circuit (16mm SWA, 33A total load, 75m run, armour is much more than sufficient). There are no extraneous items in the workshop that need bonding, so my view (heavily based on the opinions of this forum) is that it is perfectly safe to take the supply earth out to the workshop. For info, the workshop is wooden construction on a concrete base.
Now I think I can see where my tutor is coming from about safety. If there was a lost neutral all earthed parts would become live. This might not be a big issue in the main building, but maybe there is a chance of someone using a metal tool outside the workshop and is stood directly on the ground. Then we'd have an issue.
So, I was thinking that a rod is not strictly needed by the letter of the law, but the more I ponder it the more I think it might be a sensible idea to put a rod in.
Just wanting peoples thoughts?