regardless of any interpretation of the regs, there is always the proviso of following the manufacturers instructions. SMA say bond, so it needs bonding, as per 7671 with 10mm.
You cannot bond using the earth (CPC) from the T&E (which, at 2.5mm is too small as well, have a look in the SMA manual).
They have used the wrong brackets so anything to overcome that will be a bodge. Trimming will help, but it's not ideal. They should have used a bracket something like these from K2
You cannot bond using the earth (CPC) from the T&E (which, at 2.5mm is too small as well, have a look in the SMA manual).
They have used the wrong brackets so anything to overcome that will be a bodge. Trimming will help, but it's not ideal. They should have used a bracket something like these from K2